WebCoRE Piston stopped working, need help
This has been working for over a year. I'm not sure if it was a recent update that broke it or what happened. To clarify that the light does turn on sometimes when the door is opened. And it does turn on with motion. The issue appears to be that sometimes/most of the time the light won't come on when the door is opened.
What I like about this piston is that if I open the door but no motion is detected the light goes off after 5 seconds. If there is a way to build this in Room Lighting or Rule Machine I'm open to that option.
Thanks in advance for the help!
I expect the exit's are causing you problems as you are not crossing the tracking trigger comparisons on each execution.
Tracking comparisons require the trigger comparison is crossed on each execution, so that the old value can be tracked for future runs.
  • in this example the exit is causing the tracking trigger comparisons to not be crossed.
  • you could set piston state if you want to have the reason tracked in state (vs. using the exit)
See:
  • if you put in an exit statement in the piston, this may cause statements below the exit to not be crossed over, that may affect the trigger comparison tracking adversely (for those statements that are below the exit).
While a warning is not generated, this is another case of the warnings:
and
I would also suggest following the request to post logs of the error you are seeing:
@nh.schottfam thank you for the information. I should've clarified I didn't write this originally and I'm not capable of writing something at this level. :grin:
I did however read thru what you sent, but I don't understand most of it.
I did remove the exit statements, and the behavior seems to be the same. I say seems to be because before I removed the exit statements it failed to turn on the light most of the time. Without the exit statements it appears to work every other time.
The interesting piece to me is that I have another piston that is exactly the same for a different door/lights that also stopped working, The only changes I've made are to update Hubitat and WebCoRE.
Should show full logs for a run or two of the piston so can see what is happening.
This is a log from when it worked.
11/7/2022, 6:49:59 PM +676ms
+3ms ╔Received event [Hubitat].time = 1667868599624 with a delay of 52ms, canQueue: true, calledMyself: false
+11ms ║RunTime initialize > 10 LockT > 1ms > r9T > 2ms > pistonT > 0ms (first state access 7 4 6)
+13ms ║Runtime (8997 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+19ms ║╔Execution stage started
+26ms ║║Condition #15 evaluated true (1ms)
+29ms ║║Comparison (boolean) false is (boolean) true = false (1ms)
+30ms ║║Condition #16 evaluated false (3ms)
+31ms ║║Condition group #14 evaluated false (condition did not change) (6ms)
+31ms ║║Condition group #9 evaluated false (condition did not change) (7ms)
+36ms ║║Condition #22 evaluated false (3ms)
+36ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+40ms ║╚Execution stage complete. (20ms)
+42ms ╚Event processed successfully (40ms)
11/7/2022, 6:49:54 PM +583ms
+3ms ╔Received event [Hubitat].time = 1667868594531 with a delay of 52ms, canQueue: true, calledMyself: false
+11ms ║RunTime initialize > 10 LockT > 1ms > r9T > 2ms > pistonT > 1ms (first state access 7 4 6)
+13ms ║Runtime (8992 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+26ms ║║Condition #11 evaluated true (1ms)
+30ms ║║Condition #12 evaluated false (3ms)
+30ms ║║Condition group #10 evaluated false (condition did not change) (6ms)
+39ms ║║Comparison (enum) closed stays (string) closed = true (1ms)
+42ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 15 wake up at Mon, Nov 7 2022 @ 6:49:59 PM CST (in 4999ms) for 15 (st:15)
+44ms ║║Condition #15 evaluated false (13ms)
+45ms ║║Condition group #14 evaluated false (condition did not change) (13ms)
+45ms ║║Condition group #9 evaluated false (condition did not change) (21ms)
+49ms ║║Condition #22 evaluated false (3ms)
+50ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+55ms ║╚Execution stage complete. (35ms)
+95ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:59 PM CST (in 5014ms)
+97ms ╚Event processed successfully (94ms)
11/7/2022, 6:49:09 PM +646ms
+4ms ╔Received event [Hubitat].time = 1667868549586 with a delay of 60ms, canQueue: true, calledMyself: false
+12ms ║RunTime initialize > 12 LockT > 0ms > r9T > 2ms > pistonT > 0ms (first state access 10 4 8)
+15ms ║Runtime (8987 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+21ms ║╔Execution stage started
+28ms ║║Condition #15 evaluated true (1ms)
+31ms ║║Comparison (boolean) false is (boolean) true = false (2ms)
+33ms ║║Condition #16 evaluated false (3ms)
+33ms ║║Condition group #14 evaluated false (condition did not change) (7ms)
+34ms ║║Condition group #9 evaluated false (condition did not change) (8ms)
+42ms ║║Comparison (enum) off changes_to (string) off = false (0ms)
+43ms ║║Condition #22 evaluated false (8ms)
+44ms ║║Condition group #21 evaluated false (condition did not change) (9ms)
+49ms ║╚Execution stage complete. (29ms)
+98ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:54 PM CST (in 44864ms)
+100ms ╚Event processed successfully (97ms)
11/7/2022, 6:49:04 PM +545ms
+2ms ╔Received event [Garage Main Lights].switch = off with a delay of 66ms, canQueue: false, calledMyself: true
+5ms ║RunTime initialize > 4 LockT > 0ms > r9T > 2ms > pistonT > 1ms (first state access 2 2 2)
+7ms ║Runtime (8938 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+9ms ║╔Execution stage started
+15ms ║║Comparison (enum) off is (string) off = true (0ms)
+16ms ║║Condition #2 evaluated true (5ms)
+20ms ║║Condition #4 evaluated false (2ms)
+24ms ║║Condition #5 evaluated false (4ms)
+26ms ║║Condition group #3 evaluated false (condition changed) (9ms)
+26ms ║║Condition group #1 evaluated false (condition did not change) (16ms)
+31ms ║║Comparison (enum) inactive stays (string) inactive = true (1ms)
+33ms ║║Doing nothing found timed trigger schedule stays result true found timer for condition 11
+34ms ║║Condition #11 evaluated false (7ms)
+35ms ║║Condition group #10 evaluated false (condition did not change) (8ms)
+42ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 15 wake up at Mon, Nov 7 2022 @ 6:49:09 PM CST (in 4999ms) for 15 (st:15)
+44ms ║║Condition #15 evaluated false (8ms)
+46ms ║║Condition group #14 evaluated false (condition changed) (10ms)
+47ms ║║Condition group #9 evaluated false (condition changed) (20ms)
+51ms ║║Comparison (enum) off changes_to (string) off = false (0ms)
+52ms ║║Condition #22 evaluated false (3ms)
+52ms ║║Condition group #21 evaluated false (condition did not change) (5ms)
+78ms ║╚Execution stage complete. (70ms)
+115ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:09 PM CST (in 4991ms),with 1 more job pending
+117ms ╚Event processed successfully (115ms)
11/7/2022, 6:49:04 PM +348ms
+4ms ╔Received event [Hubitat].time = 1667868544290 with a delay of 58ms, canQueue: true, calledMyself: false
+12ms ║RunTime initialize > 11 LockT > 0ms > r9T > 2ms > pistonT > 1ms (first state access 9 4 7)
+14ms ║Runtime (8974 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+20ms ║╔Execution stage started
+27ms ║║Condition #15 evaluated true (1ms)
+29ms ║║Comparison (boolean) true is (boolean) true = true (1ms)
+31ms ║║Condition #16 evaluated true (4ms)
+70ms ║║Duration 3761060ms for is >= 60000ms threshold = true
+71ms ║║Comparison (enum) inactive was (string) inactive = true (30ms)
+72ms ║║Condition #17 evaluated true (40ms)
+73ms ║║Condition group #14 evaluated true (condition changed) (48ms)
+75ms ║║Condition group #9 evaluated true (condition changed) (50ms)
+107ms ║║Executed physical command [Garage Main Lights].off() (28ms)
+112ms ║║Executed virtual command [Garage Main Lights].setVariable (1ms)
+116ms ║║Condition #22 evaluated false (3ms)
+118ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+124ms ║╚Execution stage complete. (104ms)
+178ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:54 PM CST (in 50087ms)
+179ms ╚Event processed successfully (176ms)
11/7/2022, 6:49:04 PM +507ms
+3ms ╔Received event [Garage Main Lights].switch = off with a delay of 28ms, canQueue: true, calledMyself: false
+5ms ╚Event queued (1ms)
11/7/2022, 6:48:59 PM +255ms
+3ms ╔Received event [Family Room Door Contact].contact = closed with a delay of 34ms, canQueue: true, calledMyself: false
+11ms ║RunTime initialize > 10 LockT > 0ms > r9T > 2ms > pistonT > 1ms (first state access 8 4 6)
+13ms ║Runtime (8981 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+14ms ║╔Execution stage started
+20ms ║║Comparison (enum) on is (string) off = false (0ms)
+21ms ║║Condition #2 evaluated false (4ms)
+21ms ║║Condition group #1 evaluated false (condition did not change) (5ms)
+26ms ║║Comparison (enum) inactive stays (string) inactive = true (1ms)
+28ms ║║Doing nothing found timed trigger schedule stays result true found timer for condition 11
+29ms ║║Condition #11 evaluated false (7ms)
+30ms ║║Condition group #10 evaluated false (condition did not change) (7ms)
+34ms ║║Comparison (enum) closed stays (string) closed = true (0ms)
+37ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 15 wake up at Mon, Nov 7 2022 @ 6:49:04 PM CST (in 4999ms) for 15 (st:15)
+38ms ║║Condition #15 evaluated false (7ms)
+38ms ║║Condition group #14 evaluated false (condition did not change) (8ms)
+39ms ║║Condition group #9 evaluated false (condition did not change) (17ms)
+43ms ║║Condition #22 evaluated false (3ms)
+44ms ║║Condition group #21 evaluated false (condition did not change) (3ms)
+68ms ║╚Execution stage complete. (53ms)
+103ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:04 PM CST (in 4995ms),with 1 more job pending
+105ms ╚Event processed successfully (102ms)
11/7/2022, 6:48:54 PM +647ms
+2ms ╔Received event [Garage Main Lights].switch = on with a delay of 104ms, canQueue: false, calledMyself: true
+7ms ║Runtime (8914 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+15ms ║║Comparison (enum) on is (string) off = false (0ms)
+16ms ║║Condition #2 evaluated false (5ms)
+18ms ║║Condition group #1 evaluated false (condition changed) (6ms)
+23ms ║║Comparison (enum) inactive stays (string) inactive = true (0ms)
+25ms ║║Doing nothing found timed trigger schedule stays result true found timer for condition 11
+25ms ║║Condition #11 evaluated false (6ms)
+26ms ║║Condition group #10 evaluated false (condition did not change) (7ms)
+30ms ║║Comparison (enum) open stays (string) closed = false (1ms)
+32ms ║║Canceling any timed trigger schedule stays result false cancel any timers for condition 15
+34ms ║║Condition #15 evaluated false (7ms)
+35ms ║║Condition group #14 evaluated false (condition did not change) (8ms)
+35ms ║║Condition group #9 evaluated false (condition did not change) (17ms)
+39ms ║║Comparison (enum) on changes_to (string) off = false (0ms)
+40ms ║║Condition #22 evaluated false (3ms)
+41ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+66ms ║╚Execution stage complete. (58ms)
+111ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:54 PM CST (in 59845ms)
+112ms ╚Event processed successfully (111ms)
11/7/2022, 6:48:54 PM +381ms
+3ms ╔Received event [Family Room Door Contact].contact = open with a delay of 33ms, canQueue: true, calledMyself: false
+55ms ║RunTime initialize > 54 LockT > 1ms > r9T > 48ms > pistonT > 47ms (first state access 5 4 50)
+57ms ║Runtime (8878 bytes) initialized in 48ms (v0.3.114.20220928_HE)
+59ms ║╔Execution stage started
+65ms ║║Comparison (enum) off is (string) off = true (1ms)
+66ms ║║Condition #2 evaluated true (4ms)
+69ms ║║Condition #4 evaluated false (3ms)
+73ms ║║Comparison (enum) open changes_to (string) open = true (0ms)
+77ms ║║Condition #5 evaluated true (7ms)
+79ms ║║Condition group #3 evaluated true (condition changed) (13ms)
+81ms ║║Condition group #1 evaluated true (condition changed) (20ms)
+135ms ║║Executed physical command [Garage Main Lights].on() (49ms)
+141ms ║║Executed virtual command [Garage Main Lights].setVariable (1ms)
+146ms ║║Comparison (enum) inactive stays (string) inactive = true (1ms)
+152ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 11 wake up at Mon, Nov 7 2022 @ 6:49:54 PM CST (in 59999ms) for 11 (st:11)
+153ms ║║Condition #11 evaluated false (11ms)
+154ms ║║Condition group #10 evaluated false (condition did not change) (12ms)
+158ms ║║Comparison (enum) open stays (string) closed = false (1ms)
+161ms ║║Canceling any timed trigger schedule stays result false cancel any timers for condition 15
+164ms ║║Condition #15 evaluated false (8ms)
+165ms ║║Condition group #14 evaluated false (condition did not change) (9ms)
+166ms ║║Condition group #9 evaluated false (condition did not change) (23ms)
+177ms ║║Condition #22 evaluated false (9ms)
+177ms ║║Condition group #21 evaluated false (condition did not change) (10ms)
+186ms ║╚Execution stage complete. (128ms)
+247ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:49:54 PM CST (in 59987ms)
+249ms ╚Event processed successfully (246ms)
This is a log from when it didn't work
11/7/2022, 6:54:17 PM +896ms
+3ms ╔Received event [Hubitat].time = 1667868857843 with a delay of 53ms, canQueue: true, calledMyself: false
+12ms ║RunTime initialize > 12 LockT > 0ms > r9T > 2ms > pistonT > 1ms (first state access 10 4 8)
+15ms ║Runtime (8985 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+31ms ║║Comparison (boolean) false is (boolean) true = false (1ms)
+32ms ║║Condition #16 evaluated false (3ms)
+33ms ║║Condition group #14 evaluated false (condition did not change) (6ms)
+34ms ║║Condition group #9 evaluated false (condition did not change) (7ms)
+38ms ║║Condition #22 evaluated false (4ms)
+39ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+42ms ║╚Execution stage complete. (21ms)
+45ms ╚Event processed successfully (42ms)
11/7/2022, 6:54:12 PM +807ms
+3ms ╔Received event [Hubitat].time = 1667868852746 with a delay of 61ms, canQueue: true, calledMyself: false
+13ms ║Runtime (8979 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+25ms ║║Condition #11 evaluated true (1ms)
+28ms ║║Comparison (boolean) false is (boolean) true = false (1ms)
+29ms ║║Condition #12 evaluated false (3ms)
+30ms ║║Condition group #10 evaluated false (condition did not change) (5ms)
+34ms ║║Comparison (enum) closed stays (string) closed = true (1ms)
+38ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 15 wake up at Mon, Nov 7 2022 @ 6:54:17 PM CST (in 4999ms) for 15 (st:15)
+40ms ║║Condition #15 evaluated false (9ms)
+40ms ║║Condition group #14 evaluated false (condition did not change) (10ms)
+41ms ║║Condition group #9 evaluated false (condition did not change) (17ms)
+45ms ║║Condition #22 evaluated false (3ms)
+46ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+50ms ║╚Execution stage complete. (32ms)
+111ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:54:17 PM CST (in 5014ms)
+113ms ╚Event processed successfully (110ms)
11/7/2022, 6:53:24 PM +936ms
+4ms ╔Received event [Hubitat].time = 1667868804881 with a delay of 55ms, canQueue: true, calledMyself: false
+15ms ║Runtime (8975 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+32ms ║║Condition group #14 evaluated false (condition did not change) (6ms)
+33ms ║║Condition group #9 evaluated false (condition did not change) (8ms)
+41ms ║║Condition #22 evaluated false (7ms)
+42ms ║║Condition group #21 evaluated false (condition did not change) (8ms)
+47ms ║╚Execution stage complete. (27ms)
+87ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:54:12 PM CST (in 47791ms)
+88ms ╚Event processed successfully (85ms)
11/7/2022, 6:53:19 PM +838ms
+3ms ╔Received event [Family Room Door Contact].contact = closed with a delay of 21ms, canQueue: true, calledMyself: false
+10ms ║RunTime initialize > 9 LockT > 1ms > r9T > 2ms > pistonT > 0ms (first state access 6 4 5)
+12ms ║Runtime (8966 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+19ms ║║Comparison (enum) off is (string) off = true (1ms)
+20ms ║║Condition #2 evaluated true (4ms)
+24ms ║║Condition #4 evaluated false (3ms)
+27ms ║║Comparison (enum) closed changes_to (string) open = false (1ms)
+28ms ║║Condition #5 evaluated false (4ms)
+29ms ║║Condition group #3 evaluated false (condition did not change) (8ms)
+29ms ║║Condition group #1 evaluated false (condition did not change) (14ms)
+34ms ║║Comparison (enum) inactive stays (string) inactive = true (1ms)
+36ms ║║Doing nothing found timed trigger schedule stays result true found timer for condition 11
+37ms ║║Condition #11 evaluated false (7ms)
+38ms ║║Condition group #10 evaluated false (condition did not change) (7ms)
+42ms ║║Comparison (enum) closed stays (string) closed = true (0ms)
+45ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 15 wake up at Mon, Nov 7 2022 @ 6:53:24 PM CST (in 4999ms) for 15 (st:15)
+46ms ║║Condition #15 evaluated false (7ms)
+46ms ║║Condition group #14 evaluated false (condition did not change) (8ms)
+47ms ║║Condition group #9 evaluated false (condition did not change) (16ms)
+51ms ║║Condition #22 evaluated false (2ms)
+52ms ║║Condition group #21 evaluated false (condition did not change) (4ms)
+78ms ║╚Execution stage complete. (65ms)
+119ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:53:24 PM CST (in 4992ms),with 1 more job pending
+121ms ╚Event processed successfully (118ms)
11/7/2022, 6:53:12 PM +710ms
+3ms ╔Received event [Family Room Door Contact].contact = open with a delay of 28ms, canQueue: true, calledMyself: false
+9ms ║RunTime initialize > 9 LockT > 0ms > r9T > 2ms > pistonT > 1ms (first state access 7 4 5)
+12ms ║Runtime (8894 bytes) initialized in 2ms (v0.3.114.20220928_HE)
+13ms ║╔Execution stage started
+20ms ║║Condition #2 evaluated true (5ms)
+24ms ║║Condition #4 evaluated false (2ms)
+27ms ║║Comparison (enum) open changes_to (string) open = false (0ms)
+37ms ║║Adding a timed trigger schedule stays result true scheduling timer for condition 11 wake up at Mon, Nov 7 2022 @ 6:54:12 PM CST (in 59999ms) for 11 (st:11)
+39ms ║║Condition #11 evaluated false (9ms)
+40ms ║║Condition group #10 evaluated false (condition did not change) (9ms)
+44ms ║║Comparison (enum) open stays (string) closed = false (0ms)
+45ms ║║Canceling any timed trigger schedule stays result false cancel any timers for condition 15
+48ms ║║Condition #15 evaluated false (7ms)
+48ms ║║Condition group #14 evaluated false (condition did not change) (8ms)
+49ms ║║Condition group #9 evaluated false (condition did not change) (19ms)
+53ms ║║Condition #22 evaluated false (3ms)
+54ms ║║Condition group #21 evaluated false (condition did not change) (3ms)
+59ms ║╚Execution stage complete. (46ms)
+91ms ║Setting up scheduled job for Mon, Nov 7 2022 @ 6:54:12 PM CST (in 60005ms)
+93ms ╚Event processed successfully (90ms)
So this was fixed with an update to webCoRE.
Also see:
Thanks @nh.schottfam that explanation of the triggers is very helpful.