Just added a Sinope Load Controller RM3250ZB to my HE and it will not send the power attribute unless I command a refresh. I have to wonder if the newly implemented 2.4.1.151 wattage setting is not working correctly and mine is set on 5000 watts or something which I don't reach. @mike.maxwell@gopher.ny
Maybe something I am missing?
When I go to configure it with debug on there is no indication that anything has been written to the device, just catchalls followed by the refresh.
Being an older driver the power reporting configuration acknowledgment isn't currently logged.
You do need to pick a power threshold that your device that's being monitored will exceed...
Also, saving the preference setting is all that's needed to update the threshold, there is no need to click configure.
Configure will actually turn the reporting off...
This is the reason. The Sinope Water Heater Controller RM3500ZB, behaves the same way. Just switch to the in-built load controller driver and click Save, but do not click "Configure".
All working as it should now. Thanks.
Curious, is the configure button press turning off the power reporting intended behavior? I would have never thought that would be the issue, but sure enough it was.