I would love some feedback and hopefully also points for improvement on my multi floor/room heating automation.

The situation, pretty typical:

  • central heating with radiators
  • a single 'proper' thermostat in the living room
  • additionally 3 bedrooms, 1 home office that i mostly care about heating or not
  • all rooms have really dynamic use, so hard to even think of a schedule, let alone automate it.
  • all rooms have a zigbee thermostattemperature/humidity sensor

Current state with a lot of help from members here:

  • using the Honeywell Thermostat App to control the central heating
  • using the thermostat scheduler to set the temperature per mode (Away, Morning, Day, Evening, Night)
  • using the thermostat controller to set up per mode which room thermostatstemperature sensors are read and averaged/weighted

Last winter this worked better than any of the 4 years before, so it was a huge QoL improvement. However, as expected, i am at the next stage of optimizing this, mainly looking at rooms that are used few hours per some days. I picked the home office as such.

Sometimes we work 10 hours a day in it, sometimes not at all, sometimes we start there and move to another room with the work laptop.

So choices are to either leave it out of the thermostat controller and hope it passively stays warm, or to keep adding and removing it from the mode. Or, as i just found out 10 hours ago - use a variable for the weight. That is amazing, so i set up a button to set the office multiplier to either 0 or 1.

My questions:

  1. How do i prevent the office staying ON until i click the OFF button? I am thinking it should be easy and obvious but like last year i knew nothing about the thermostats, now i don't know how to set a timer and how to make sure i set/reset it. I can see a lot of edge cases...
  2. If anyone is using a similar setup to me (thermostat scheduler/controller) i can use some help in all the variables, i.e. hysteresis, control Offset, Thermostat mode, Required separation, Refresh interval... Most of those i got by trial and error, so i would love to get a more concise and practical knowledge on.
  3. I have push notifications to my phone to tell me the operating state of the actual thermostat. It took me months to figure out what combination of variables i need to monitor to know when the heating is using gas. However, when temps get to the desired level, i start to get spammed every 5 minutes about the heating being ON/OFF/ON/OFF... Any help would be highly welcome to solve that while keeping the temps at the desired level. I tried setting the Hysteresis, Control offset, Weights, all the highlighted values lower, without much success. Even tried setting some extremes like 3C or 0.1C.

Some screenshots:

  1. Mode Manager:
    image
  2. Thermostat scheduler:
  3. Thermostat controller:
    a. It has temperature sensors in each room named as the room, so literally 'Master Bedroom' instead of 'Master Bedroom Temperature and Humidity Sensor'.

Hoping to get some feedback for improving this and mainly resetting the office multiplier on inactivity (i am thinking of a train's dead-man switch or what's the name?). So, if i don't press the switch for say 60 or 90 minutes, the multiplier goes to 0 (no heating).

Edit:
#1 - remove the wrongly used thermostat word where i meant temperature sensor.
#2 - added a clarification in bold

You have a lot going on there. The first thing that came to mind was using a presence sensor in the office, to determine when you are there or not, to change your multiplier variable separately in a rule.

My knowledge on presence sensors is basically either a button i push, or there was some nfc thing with the phone being set on a sticker on the desk, or infrared ones. I think i read the infrared ones are not good for the health?.

Is there a safe and simple option?

Oh, I mean mmWave Presence (motion) sensors. They detect micro movements, unlike the PIR sensors that only see large movements. I put one in my office for lights to go on and off when I enter or leave. It never turns the lights off while I am present in my office. They picked up the term presence because they detect the presence of people, not just motion in the room.

I also use them to control what remote temp sensor is to be used for the thermostat based on what room has people present in it, since the thermostat is in the hallway downstairs where my office and home theater are located.

Thanks, i have a new word to research now. Sounds like a great addition to a smarter home.

Is this more of a geek out project VS a cost savings project?

Not sure which Honeywell thermostats you have, but Honeywell does offer occupancy sensors to work with some of their thermostats similar to Ecobee sensors. Keeping your heating controlled by one system can be smart.

Blockquote

Could very well be, although it started with the need to warm up the bathroom for bathing a baby while the temp outside was -10 C, the living room was at 21 C and the bathroom at 18 C. Short of me opening the livingroom doors and windows wide and setting the thermostat to 25 C, the above was the only solution i could think of.

I have the Honeywell Lyric T6. No idea what options it has, If you do - please let me know. I will in any case investigate what you said.

Thanks!

Heating / Cooling down here (for me) is much simpler with a ducted system that covers the whole house (admittedly for me a single level with Kitchen/Dining/Living and 3 bedrooms separated by a Hallway).

Regardless, I would still question whether heating/cooling each room regardless of the occupancy or usage actually affects the overall power usage for heating/cooling? I.e. is it cheaper to heat/cool the whole home regardless of occupancy compared to responding to a change in occupancy and having to bring a room to the desired temperature with a bigger gap to make up.

At the very least maintaining a moderate temparature compared to the desired temperature could be a good middle ground.

Maybe i need to clarify.

We want to have uniform temperatures across the home. I don't have radiator valves that control each radiator, so if the living room (where the thermostat is) is at the desired temperature, the entire central heating goes off. To get other rooms warmer, i need to get the living room warmer. And we don't like/stand it too warm or too cold.

So, the above complexity is the only way i can control the temperature to eventually levels out.

Am i missing something obvious?

Don't worry, I made my comment without looking too closely at your setup, only that it had been described as complex. I was only hoping to provide some encouragement to reduce the complexity... But if you feel it is necessary, then that's ok.

I'm not likely to have time at the moment to assess your automation in detail....

Perfectly fine, and thank you for trying to help me. I will keep playing with the idea to simplify it all. That is indeed the target goal.

What i just now have is that the heating is set to 20.3 C and the temperature of the virtual thermostat (combination) is at 20.7 C. And the heating is still ON, making the temperature all over the house rise.

It should (IMHO) have been OFF for the past few hours.

A lot of logs in case anyone could figure out why:

app 497 = therm controller app
dev 279 = the actual thermostat device
app 444 = the Honeywell app
app 498 = therm scheduler app
dev 304 = therm controller thermostat dev
dev 310 = livingroom temp sensor

Logs:
app:4972025-10-25 15:06:33.297info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:06:33.295info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:06:33.286info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:06:32.850info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4982025-10-25 15:06:30.981info
Heating Setpoint 20.3 from Mode Schedule: Day
app:4972025-10-25 15:06:30.878info
Controller: updateSetPoints(20.3, -)
dev:3042025-10-25 15:06:30.865info
updateSetPoints(20.3, -)
app:4972025-10-25 15:06:30.858info
Controller: setHeatingSetpoint(20.3) was called
dev:3042025-10-25 15:06:30.843info
setHeatingSetpoint(20.3) was called
app:4972025-10-25 15:05:01.319info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:05:01.317info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:05:01.309info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:05:01.076info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4982025-10-25 15:04:37.507info
Initialized
app:4972025-10-25 15:04:13.845info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:04:13.843info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:04:13.835info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:04:13.595info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 15:04:12.149info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 15:04:11.884info
setTemperature(20.7) was called
app:4972025-10-25 15:04:11.736info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:04:11.734info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:04:11.727info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:04:11.486info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 15:04:10.024info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 15:04:09.759info
setTemperature(20.7) was called
app:4972025-10-25 15:04:09.267info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 15:04:09.003info
setTemperature(20.7) was called
app:4972025-10-25 15:04:08.442info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:04:08.440info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:04:08.432info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:04:08.198info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 15:04:06.849info
Hysteresis for thermController-Livingroom: 1.0 from Manual
app:4972025-10-25 15:04:06.746info
Controller: setHysteresis(1.0) was called
dev:3042025-10-25 15:04:06.481info
setHysteresis(1.0) was called
app:4972025-10-25 15:03:10.790info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:03:10.788info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:03:10.781info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:03:10.536info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 15:03:09.072info
Office temperature = 21.25°, Average sensor temperature = 20.7°
app:4972025-10-25 15:03:09.027info
Controller: setTemperature(20.7) was called
dev:1702025-10-25 15:03:08.995info
Office pressure is 99.9kPa
dev:3042025-10-25 15:03:08.759info
setTemperature(20.7) was called
dev:1702025-10-25 15:03:08.687info
Office pressure is 99.9kPa
dev:1702025-10-25 15:03:08.640info
Office temperature is 21.25°C
app:4442025-10-25 15:02:10.647info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 15:01:18.536info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:01:18.534info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:01:18.512info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:01:18.255info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 15:01:16.354info
Livingroom temperature = 20.74°, Average sensor temperature = 20.7°
app:4972025-10-25 15:01:16.245info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 15:01:15.978info
setTemperature(20.7) was called
dev:3102025-10-25 15:01:15.909info
Livingroom pressure is 99.9kPa
dev:3102025-10-25 15:01:15.876info
Livingroom temperature is 20.74°C
app:4972025-10-25 15:00:01.265info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 15:00:01.263info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 15:00:01.250info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 15:00:00.986info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:55:01.330info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:55:01.328info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:55:01.321info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:55:01.071info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:51:53.603info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:51:53.601info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:51:53.593info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:51:53.334info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:51:51.530info
Livingroom temperature = 20.71°, Average sensor temperature = 20.7°
app:4972025-10-25 14:51:51.449info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 14:51:51.142info
setTemperature(20.7) was called
app:4972025-10-25 14:51:51.066info
Livingroom temperature = 20.73°, Average sensor temperature = 20.7°
app:4972025-10-25 14:51:50.976info
Controller: setTemperature(20.7) was called
dev:3102025-10-25 14:51:50.944info
Livingroom pressure is 99.9kPa
dev:3102025-10-25 14:51:50.943info
Livingroom temperature is 20.71°C
dev:3042025-10-25 14:51:50.647info
setTemperature(20.7) was called
dev:3102025-10-25 14:51:50.552info
Livingroom temperature is 20.73°C
app:4972025-10-25 14:50:01.816info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:50:01.814info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:50:01.806info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:50:01.564info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:48:51.470info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:48:51.468info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:48:51.460info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:48:51.251info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:48:49.546info
Office temperature = 21.20°, Average sensor temperature = 20.7°
app:4972025-10-25 14:48:49.424info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 14:48:49.157info
setTemperature(20.7) was called
app:4972025-10-25 14:48:49.085info
Office temperature = 21.15°, Average sensor temperature = 20.7°
dev:1702025-10-25 14:48:48.985info
Office pressure is 99.8kPa
app:4972025-10-25 14:48:48.983info
Controller: setTemperature(20.7) was called
dev:1702025-10-25 14:48:48.946info
Office temperature is 21.20°C
dev:3042025-10-25 14:48:48.715info
setTemperature(20.7) was called
dev:1702025-10-25 14:48:48.609info
Office temperature is 21.15°C
app:4972025-10-25 14:45:01.201info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:45:01.199info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:45:01.190info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:45:00.976info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:40:02.282info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:40:02.280info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:40:02.271info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:40:01.877info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:35:04.259info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:35:04.257info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:35:04.248info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:35:03.878info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4442025-10-25 14:33:51.364info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 14:30:03.115info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:30:03.113info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:30:03.103info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:30:00.989info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:25:01.312info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:25:01.310info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:25:01.301info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:25:01.073info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:21:02.090info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:21:02.087info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:21:02.080info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:21:01.847info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:21:00.463info
Office temperature = 21.13°, Average sensor temperature = 20.7°
app:4972025-10-25 14:21:00.408info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 14:21:00.138info
setTemperature(20.7) was called
dev:1702025-10-25 14:21:00.067info
Office pressure is 99.8kPa
dev:1702025-10-25 14:21:00.046info
Office temperature is 21.13°C
app:4972025-10-25 14:20:26.592info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:20:26.590info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:20:26.583info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:20:26.359info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:20:25.067info
Livingroom temperature = 20.68°, Average sensor temperature = 20.7°
app:4972025-10-25 14:20:24.935info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 14:20:24.663info
setTemperature(20.7) was called
dev:3102025-10-25 14:20:24.589info
Livingroom pressure is 99.9kPa
dev:3102025-10-25 14:20:24.527info
Livingroom temperature is 20.68°C
app:4972025-10-25 14:20:01.251info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:20:01.249info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:20:01.240info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:20:01.024info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:15:01.249info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:15:01.247info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:15:01.236info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:15:01.014info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:10:01.212info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:10:01.210info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:10:01.203info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:10:00.957info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:09:44.167info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:09:44.165info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:09:44.157info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:09:43.932info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:09:39.026info
Livingroom temperature = 20.65°, Average sensor temperature = 20.7°
app:4972025-10-25 14:09:38.956info
Controller: setTemperature(20.7) was called
dev:3102025-10-25 14:09:38.899info
Livingroom pressure is 99.9kPa
dev:3042025-10-25 14:09:38.667info
setTemperature(20.7) was called
dev:3102025-10-25 14:09:38.529info
Livingroom pressure is 99.9kPa
dev:3102025-10-25 14:09:38.514info
Livingroom is 61%RH
dev:3102025-10-25 14:09:38.506info
Livingroom temperature is 20.65°C
app:4442025-10-25 14:05:26.336info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 14:05:01.205info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:05:01.202info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:05:01.192info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:05:00.947info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:04:06.560info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:04:06.558info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:04:06.550info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:04:06.335info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 14:03:59.108info
Office temperature = 21.10°, Average sensor temperature = 20.7°
app:4972025-10-25 14:03:59.035info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 14:03:58.770info
setTemperature(20.7) was called
dev:1702025-10-25 14:03:58.684info
Office pressure is 99.8kPa
dev:1702025-10-25 14:03:58.647info
Office temperature is 21.10°C
app:4972025-10-25 14:00:01.395info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 14:00:01.393info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 14:00:01.382info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 14:00:01.129info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:55:07.408info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:55:07.406info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:55:07.393info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:55:06.690info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:52:42.189info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:52:42.187info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:52:42.179info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:52:41.769info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:52:40.216info
Livingroom temperature = 20.68°, Average sensor temperature = 20.7°
app:4972025-10-25 13:52:40.135info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 13:52:39.834info
setTemperature(20.7) was called
dev:3102025-10-25 13:52:39.790info
Livingroom pressure is 99.9kPa
dev:3102025-10-25 13:52:39.755info
Livingroom temperature is 20.68°C
app:4972025-10-25 13:52:34.506info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:52:34.504info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:52:34.497info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:52:33.293info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:52:30.606info
Office temperature = 21.03°, Average sensor temperature = 20.6°
dev:1702025-10-25 13:52:30.548info
Office pressure is 99.8kPa
app:4972025-10-25 13:52:30.534info
Controller: setTemperature(20.6) was called
dev:3042025-10-25 13:52:30.255info
setTemperature(20.6) was called
dev:1702025-10-25 13:52:30.178info
Office is 58%RH
dev:1702025-10-25 13:52:30.154info
Office temperature is 21.03°C
app:4972025-10-25 13:50:06.372info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:50:06.370info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:50:06.362info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:50:05.988info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:49:20.424info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:49:20.419info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:49:20.409info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:49:20.188info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:49:18.321info
Livingroom temperature = 20.64°, Average sensor temperature = 20.6°
app:4972025-10-25 13:49:18.241info
Controller: setTemperature(20.6) was called
dev:3042025-10-25 13:49:17.924info
setTemperature(20.6) was called
dev:3102025-10-25 13:49:17.880info
Livingroom pressure is 99.8kPa
dev:3102025-10-25 13:49:17.781info
Livingroom temperature is 20.64°C
dev:3102025-10-25 13:49:17.424info
Livingroom is 62%RH
dev:2792025-10-25 13:45:31.078error
org.codehaus.groovy.runtime.metaclass.MissingMethodExceptionNoStack: No signature of method: user_driver_thecloudtaylor_Honeywell_Home_Thermostat_1085.syncClock() is applicable for argument types: () values: [] (method syncClock)
app:4972025-10-25 13:45:01.239info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:45:01.237info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:45:01.227info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:45:00.918info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:40:01.403info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:40:01.399info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:40:01.391info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:40:01.155info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4442025-10-25 13:37:07.039info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 13:35:09.772info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:35:09.770info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:35:09.762info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:35:05.797info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:30:01.581info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:30:01.579info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:30:01.567info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:30:01.288info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:26:35.410info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:26:35.408info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:26:35.398info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:26:35.160info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:26:33.327info
Office temperature = 20.88°, Average sensor temperature = 20.7°
app:4972025-10-25 13:26:33.235info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 13:26:32.970info
setTemperature(20.7) was called
dev:1702025-10-25 13:26:32.920info
Office pressure is 99.8kPa
dev:1702025-10-25 13:26:32.874info
Office temperature is 20.88°C
dev:3102025-10-25 13:26:04.739info
Livingroom pressure is 99.8kPa
app:4972025-10-25 13:25:01.436info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:25:01.432info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:25:01.424info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:25:01.180info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:20:10.938info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:20:10.935info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:20:10.924info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:20:10.708info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:20:08.791info
Office temperature = 20.86°, Average sensor temperature = 20.7°
app:4972025-10-25 13:20:08.708info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 13:20:08.441info
setTemperature(20.7) was called
dev:1702025-10-25 13:20:08.401info
Office pressure is 99.7kPa
dev:1702025-10-25 13:20:08.382info
Office temperature is 20.86°C
app:4972025-10-25 13:20:01.265info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:20:01.263info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:20:01.255info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:20:01.034info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:18:23.004info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:18:23.001info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:18:22.991info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:18:22.765info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:18:20.960info
Livingroom temperature = 20.71°, Average sensor temperature = 20.7°
app:4972025-10-25 13:18:20.856info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 13:18:20.591info
setTemperature(20.7) was called
dev:3102025-10-25 13:18:20.555info
Livingroom pressure is 99.8kPa
dev:3102025-10-25 13:18:20.533info
Livingroom temperature is 20.71°C
app:4972025-10-25 13:15:12.003info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:15:12.001info
Livingroom Thermostat heating setpoint set to 19.8
app:4442025-10-25 13:15:11.778info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
dev:2792025-10-25 13:15:11.135warn
Livingroom Thermostat Set heating point failed, attempting a refresh and re-try.
app:4442025-10-25 13:15:11.130error
java.net.SocketTimeoutException: Read timed out on line 679 (method setThermosatSetPoint)
app:4442025-10-25 13:15:01.049info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:10:54.075info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:10:54.073info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:10:54.065info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:10:53.849info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:10:52.447info
Office temperature = 20.78°, Average sensor temperature = 20.8°
app:4972025-10-25 13:10:52.329info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 13:10:52.064info
setTemperature(20.8) was called
dev:1702025-10-25 13:10:52.006info
Office temperature is 20.78°C
dev:1702025-10-25 13:10:51.999info
Office pressure is 99.7kPa
app:4972025-10-25 13:10:01.232info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:10:01.230info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:10:01.222info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:10:00.895info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4442025-10-25 13:08:47.297info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 13:07:57.576info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:07:57.574info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:07:57.567info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:07:57.341info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:07:55.517info
Livingroom temperature = 20.75°, Average sensor temperature = 20.8°
app:4972025-10-25 13:07:55.405info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 13:07:55.132info
setTemperature(20.8) was called
dev:3102025-10-25 13:07:55.058info
Livingroom pressure is 99.8kPa
dev:3102025-10-25 13:07:55.036info
Livingroom temperature is 20.75°C
app:4972025-10-25 13:05:03.372info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:05:03.370info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:05:03.362info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:05:02.011info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:05:01.591info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:05:01.588info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:05:01.576info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:05:00.267info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:04:58.688info
Office temperature = 20.68°, Average sensor temperature = 20.8°
app:4972025-10-25 13:04:58.512info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 13:04:58.141info
setTemperature(20.8) was called
dev:1702025-10-25 13:04:58.057info
Office pressure is 99.7kPa
dev:1702025-10-25 13:04:57.967info
Office temperature is 20.68°C
app:4972025-10-25 13:04:41.076info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:04:41.073info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:04:41.064info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:04:40.651info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:04:33.440info
Livingroom temperature = 20.79°, Average sensor temperature = 20.8°
app:4972025-10-25 13:04:33.346info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 13:04:33.056info
setTemperature(20.8) was called
dev:3102025-10-25 13:04:33.025info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 13:04:33.004info
Livingroom temperature is 20.79°C
app:4972025-10-25 13:02:57.391info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:02:57.389info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:02:57.382info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:02:54.227info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:02:52.299info
Livingroom temperature = 20.85°, Average sensor temperature = 20.9°
app:4972025-10-25 13:02:52.210info
Controller: setTemperature(20.9) was called
dev:3042025-10-25 13:02:51.946info
setTemperature(20.9) was called
dev:3102025-10-25 13:02:51.876info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 13:02:51.853info
Livingroom temperature is 20.85°C
app:4972025-10-25 13:02:33.642info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:02:33.640info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:02:33.634info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:02:33.258info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:02:31.853info
Livingroom temperature = 20.80°, Average sensor temperature = 20.8°
app:4972025-10-25 13:02:31.695info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 13:02:31.430info
setTemperature(20.8) was called
dev:3102025-10-25 13:02:31.389info
Livingroom pressure is 99.8kPa
dev:3102025-10-25 13:02:31.370info
Livingroom temperature is 20.80°C
app:4972025-10-25 13:02:19.191info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:02:19.188info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:02:19.179info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:02:18.752info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 13:02:16.244info
Office temperature = 20.64°, Average sensor temperature = 21.0°
app:4972025-10-25 13:02:16.185info
Controller: setTemperature(21.0) was called
dev:3042025-10-25 13:02:15.879info
setTemperature(21.0) was called
app:4972025-10-25 13:02:15.821info
Office temperature = 20.63°, Average sensor temperature = 21.0°
dev:1702025-10-25 13:02:15.762info
Office pressure is 99.6kPa
dev:1702025-10-25 13:02:15.757info
Office temperature is 20.64°C
app:4972025-10-25 13:02:15.735info
Controller: setTemperature(21.0) was called
dev:3042025-10-25 13:02:15.398info
setTemperature(21.0) was called
dev:1702025-10-25 13:02:15.338info
Office is 57%RH
dev:1702025-10-25 13:02:15.320info
Office temperature is 20.63°C
app:4972025-10-25 13:00:04.526info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 13:00:04.524info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 13:00:04.513info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 13:00:01.669info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:55:01.310info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:55:01.308info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:55:01.301info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:55:01.075info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:53:49.215info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:53:49.213info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:53:49.206info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:53:48.976info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:53:47.143info
Livingroom temperature = 20.96°, Average sensor temperature = 21.0°
app:4972025-10-25 12:53:47.102info
Controller: setTemperature(21.0) was called
dev:3042025-10-25 12:53:46.829info
setTemperature(21.0) was called
dev:3102025-10-25 12:53:46.790info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 12:53:46.769info
Livingroom temperature is 20.96°C
dev:3102025-10-25 12:53:46.415info
Livingroom pressure is 99.7kPa
app:4972025-10-25 12:50:01.304info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:50:01.302info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:50:01.292info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:50:01.051info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:47:35.793info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:47:35.791info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:47:35.784info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:47:35.351info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:47:33.485info
Livingroom temperature = 20.95°, Average sensor temperature = 21.0°
app:4972025-10-25 12:47:33.409info
Controller: setTemperature(21.0) was called
dev:3042025-10-25 12:47:33.145info
setTemperature(21.0) was called
dev:3102025-10-25 12:47:33.098info
Livingroom pressure is 99.7kPa
app:4972025-10-25 12:47:33.082info
Livingroom temperature = 20.99°, Average sensor temperature = 21.0°
dev:3102025-10-25 12:47:33.044info
Livingroom temperature is 20.95°C
app:4972025-10-25 12:47:32.993info
Controller: setTemperature(21.0) was called
dev:3042025-10-25 12:47:32.721info
setTemperature(21.0) was called
dev:3102025-10-25 12:47:32.676info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 12:47:32.655info
Livingroom temperature is 20.99°C
app:4972025-10-25 12:45:04.654info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:45:04.651info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:45:04.636info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:45:04.349info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:43:25.070info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:43:25.068info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:43:25.061info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:43:24.800info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:43:22.989info
Office temperature = 20.72°, Average sensor temperature = 20.8°
app:4972025-10-25 12:43:22.926info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 12:43:22.658info
setTemperature(20.8) was called
dev:1702025-10-25 12:43:22.615info
Office pressure is 99.6kPa
dev:1702025-10-25 12:43:22.590info
Office temperature is 20.72°C
app:4442025-10-25 12:40:27.574info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 12:40:02.549info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:40:02.547info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:40:02.540info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:40:02.121info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:35:01.155info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:35:01.153info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:35:01.143info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:35:00.899info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:30:01.450info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:30:01.448info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:30:01.441info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:30:01.203info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:29:44.752info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:29:44.750info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:29:44.741info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:29:44.479info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:29:43.160info
Livingroom temperature = 20.82°, Average sensor temperature = 20.8°
app:4972025-10-25 12:29:43.070info
Controller: setTemperature(20.8) was called
dev:3042025-10-25 12:29:42.782info
setTemperature(20.8) was called
dev:3102025-10-25 12:29:42.734info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 12:29:42.727info
Livingroom is 63%RH
dev:3102025-10-25 12:29:42.714info
Livingroom temperature is 20.82°C
app:4972025-10-25 12:29:25.578info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:29:25.576info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:29:25.568info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:29:25.337info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:29:23.431info
Office temperature = 20.87°, Average sensor temperature = 20.7°
app:4972025-10-25 12:29:23.374info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 12:29:23.095info
setTemperature(20.7) was called
dev:1702025-10-25 12:29:23.058info
Office pressure is 99.6kPa
dev:1702025-10-25 12:29:23.036info
Office temperature is 20.87°C
app:4972025-10-25 12:25:01.771info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:25:01.768info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:25:01.749info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:25:01.461info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:22:20.962info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:22:20.960info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:22:20.953info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:22:20.423info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:22:18.544info
Office temperature = 20.93°, Average sensor temperature = 20.7°
app:4972025-10-25 12:22:18.498info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 12:22:18.233info
setTemperature(20.7) was called
dev:1702025-10-25 12:22:18.134info
Office pressure is 99.6kPa
dev:1702025-10-25 12:22:18.105info
Office temperature is 20.93°C
app:4972025-10-25 12:20:01.296info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:20:01.294info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:20:01.287info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:20:01.063info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:19:21.813info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:19:21.811info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:19:21.804info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:19:19.604info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:19:17.643info
Livingroom temperature = 20.73°, Average sensor temperature = 20.7°
app:4972025-10-25 12:19:17.510info
Controller: setTemperature(20.7) was called
dev:3042025-10-25 12:19:17.245info
setTemperature(20.7) was called
dev:3102025-10-25 12:19:17.203info
Livingroom pressure is 99.7kPa
dev:3102025-10-25 12:19:17.188info
Livingroom is 62%RH
dev:3102025-10-25 12:19:17.181info
Livingroom temperature is 20.73°C
app:4972025-10-25 12:15:01.421info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:15:01.419info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:15:01.411info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:15:01.104info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4442025-10-25 12:12:08.180info
Honeywell API Token Refreshed Succesfully, Next Scheduled in: 1699 sec
app:4972025-10-25 12:11:53.859info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:11:53.857info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:11:53.850info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:11:53.351info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200
app:4972025-10-25 12:11:51.453info
Office temperature = 21.07°, Average sensor temperature = 20.6°
app:4972025-10-25 12:11:51.391info
Controller: setTemperature(20.6) was called
dev:3042025-10-25 12:11:51.124info
setTemperature(20.6) was called
app:4972025-10-25 12:11:51.064info
Office temperature = 21.10°, Average sensor temperature = 20.6°
app:4972025-10-25 12:11:51.014info
Controller: setTemperature(20.6) was called
dev:1702025-10-25 12:11:50.986info
Office pressure is 99.5kPa
dev:1702025-10-25 12:11:50.955info
Office temperature is 21.07°C
dev:3042025-10-25 12:11:50.710info
setTemperature(20.6) was called
dev:1702025-10-25 12:11:50.626info
Office temperature is 21.10°C
dev:3102025-10-25 12:10:12.406info
Livingroom pressure is 99.6kPa
app:4972025-10-25 12:10:05.060info
Livingroom Thermostat setting to idle by setpoint below temperature
app:4972025-10-25 12:10:05.058info
Livingroom Thermostat heating setpoint set to 19.8
dev:2792025-10-25 12:10:05.050info
Livingroom Thermostat Heating setpoint changed to 19.8
app:4442025-10-25 12:10:04.697info
SetThermostate() Mode: Heat; Heatsetpoint: 19.8; CoolPoint: 16 API Response: 200

Any help is welcome in figguring out what i missconfigured.

And there is the challenge.

Do you have manual restriction valves that can help balance the system?

I don't have radiator valves that control each radiator - Totally agree that's the core issue!

You need some sort of flow controls to dispatch the heat to the proper radiators - Have you looked at assorted TRV valves, aka: SONOFF Zigbee Thermostatic Radiator Valve | TRVZB or others?

Without a way to sense demand and control where the heat is dispatched, any "uneven temps" can't really be changed - Your just deciding what sensor to look at to raise/lower the overall temp - but the what rooms that are peaks/lows isn't going to change.

At least that's how I read all the above - You need more control points in the system to change how heat is distributed based on demand

Completely agree with the core problem.

I do have valves that in theory should support TRV. And i got 4 Honeywell HR92 Valve controllers. But when i installed them, on different radiators, one by one within 5 minutes they caused leaks on the valve pins.

Since i was doing this mid winter and i expected no issues, i since stopped trying to get them to work. I even had a plumber that set them up correctly (exact same as me) and within 2 minutes the valve pin started dripping. I tried this on 3 different TRVs in my house and will not again.

And replacing all the TRVs in the house to then risk them again leaking makes me uneasy.

So, core issue will need to stay at least this winter.

The idea to use the thermostat scheduler and controller did come from the community as a recommendation and i would like to at least understand the reason that my heating goes ON/OFF/ON/OFF every 5 minutes.

I hope someone that is using this combo can point me in the right direction.

I mean no offense if this seems basic. You should be able to manually balance the system using your sensor data.

There are loads of videos on the topic, but a quick look showed this as a pretty good one.

Doing that kind of thing first or let's say monthly over winter as temps dip will get you in a much better place for the automation.

Thanks for this video. I will definitely look into this further. The setup on my radiators is quite different, all in one on the same side, but it makes sense this applies universally. Mine has some numbers from 1 - 7 on a thing that looks like a nut around the TRV pin, so i assume it is the same thing. Down another rabbit hole.

But, regardless of the balancing, i am pretty sure i still need either proper TRVs or the apps i mentioned above if i need to have per room temps.

Yes, but we understand that didn't work for you. Manually balancing the system during winter will help first reduce one room being hot and another cold. It's the same for forced air systems. Dampers are used to reduce supply and increase supply.

I assumed you had control in each room because you said each room had zigbee thermostats.

I made a big typo on the thermostats, i see how that would skew what i wanted to say.

I do have temperature/humidity sensors, Aqara ones. Those temperature sensors are named with the room name and in the thermostat controller tables.

Apologies for the confusion, i will update the OP

No worries, friend. We are trying to help. I hope you get what you need.

I had a house with poor insulation, but it had dampers on the ducts. I marked the dampers for the ideal balance in the summer and the winter due to ac. You could do a similar thing for different stages of winter. Balance as best you can. Prove it would with your sensor data. Tune as needed. Log your radiator settings. Should be good for years to come. Just change things on schedule or if you are lucky, never again.

The T6 has the option for wired remote sensor. If you jump to a T9 or T10 you can have the wireless ones.