3phase switch recomendations

Make a screenshot of the Device Details - Data section (at the bottom of the device web page)

Was the driver selected automatically when you first paired the device to Hubitat?

Not automatically I've added the device then selected the driver the state is wrong device is on it indicates its off.
At first when I tried to operate it blinked 'on' for a sec but then went 'off' again.

1 Like

It’s a new model (another manufacturer), so it is not recognised automatically from the driver.

I will add the new manufacturer later tonight, and with a few iterations we will make it work.

1 Like

Hi Leslaw,

I hope that I have found a device profile that is the same or very close to this RTX Circuit Breaker.
It is a strange hybrid between the Tuya (Hoch) RCBO mechanic and MatSee Plus DIN Rail firmware inside .. : (

Let's first make the switch On/Off working.

  1. Update the driver to the new version 1.7.6 "2023/05/12 10:01 PM" from the dev. branch.
  2. Delete the device (the red 'REMOVE DEVICE' button at the bottom of the web page)
  3. Pair it again to HE. This driver should be selected automatically this time
  4. Turn the debug logs option on.
  5. Try switching on/off from the device web page. Is it controlled?
  6. Try switching on/off from the circuit breaker itself. Is the state reflected back to HE?
  7. Power off the device (use the other circuit breaker that feeds the AC 3 phases in) and then turn it back on.
  8. Please select all the logs as a text, copy and paste as a text here. You can use the cog wheel tool in the forum editor to hide the big logs... Or you can just send me a DM with the logs.

Sending the logs as text (not as a picture/screenshot) is very important for me because otherwise I can't simulate the messages received from the device.

Thank You for Your hard work! I've installed the new driver, but rest will have to wait till tomorrow (don't have access to the device). I'll send You the text logs after each step. Hope the cogs match:)

1 Like

Ok I didn't delete the device yet (I'll do that tomorrow) but after the driver change at least online the button works on and off reports correctly.

Debug log
dev:542023-05-12 22:34:38.448debugKompresor ignored power 1650812160 W (exceeds maximum power cap 15000 W)

dev:542023-05-12 22:34:38.443debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C813030010455455312D494F542D5A696762656500, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C8, 13, 03, 00, 10, 45, 54, 55, 31, 2D, 49, 4F, 54, 2D, 5A, 69, 67, 62, 65, 65, 00]]

dev:542023-05-12 22:34:38.438debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C813030010455455312D494F542D5A696762656500

dev:542023-05-12 22:34:38.395infoKompresor (18) AlarmSet2 : 67174575

dev:542023-05-12 22:34:38.389debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C71200000C0101006403010113040100AF, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C7, 12, 00, 00, 0C, 01, 01, 00, 64, 03, 01, 01, 13, 04, 01, 00, AF]]

dev:542023-05-12 22:34:38.383debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C71200000C0101006403010113040100AF

dev:542023-05-12 22:34:38.342errorjava.lang.NumberFormatException: null on line 1060 (method parse)

dev:542023-05-12 22:34:38.337debugKompresor (06) combined reporting data: [38, C6, 06, 00, 00, 08, 09, 10, 00, 00, 00, 00, 00, 00]

dev:542023-05-12 22:34:38.333debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C6060000080910000000000000, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C6, 06, 00, 00, 08, 09, 10, 00, 00, 00, 00, 00, 00]]

dev:542023-05-12 22:34:38.328debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C6060000080910000000000000

dev:542023-05-12 22:34:38.283infoKompresor (09) Fault : 0

dev:542023-05-12 22:34:38.279debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C50905000100, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C5, 09, 05, 00, 01, 00]]

dev:542023-05-12 22:34:38.274debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C50905000100

dev:542023-05-12 22:34:38.228debugKompresor Kompresor energy is 0.01 kWh (no change)

dev:542023-05-12 22:34:38.226debugKompresor energy_total=0.01, state.lastResetEnergy=0.0

dev:542023-05-12 22:34:38.224infoKompresor (01) Forward/Real Energy : 1 raw

dev:542023-05-12 22:34:38.221debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C40102000400000001, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C4, 01, 02, 00, 04, 00, 00, 00, 01]]

dev:542023-05-12 22:34:38.217debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C40102000400000001

dev:542023-05-12 22:34:38.175debugKompresor (16) switch : 1

dev:542023-05-12 22:34:38.172debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C31001000101, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C3, 10, 01, 00, 01, 01]]

dev:542023-05-12 22:34:38.168debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C31001000101

dev:542023-05-12 22:34:20.451debugKompresor ignored power 1650812160 W (exceeds maximum power cap 15000 W)

dev:542023-05-12 22:34:20.444debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C213030010455455312D494F542D5A696762656500, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C2, 13, 03, 00, 10, 45, 54, 55, 31, 2D, 49, 4F, 54, 2D, 5A, 69, 67, 62, 65, 65, 00]]

dev:542023-05-12 22:34:20.437debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C213030010455455312D494F542D5A696762656500

dev:542023-05-12 22:34:20.275infoKompresor (18) AlarmSet2 : 67174575

dev:542023-05-12 22:34:20.271debugKompresor parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C11200000C0101006403010113040100AF, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:AB6E, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[38, C1, 12, 00, 00, 0C, 01, 01, 00, 64, 03, 01, 01, 13, 04, 01, 00, AF]]

dev:542023-05-12 22:34:20.266debugKompresor parse: description is catchall: 0104 EF00 01 01 0040 00 AB6E 01 00 0000 02 01 38C11200000C0101006403010113040100AF

dev:542023-05-12 22:34:20.231errorjava.lang.NumberFormatException: null on line 1060 (method parse)

1 Like

Before making new tests, please update the driver again.

Also, let me know what is the approximately power of the load.

You Made some changes?

Well o the message came to late :slight_smile:

I followed the previous path and the device was found the driver was picked out of the box... unfortunettley it doesn't Control the device anymore the device is offline.

Tuya Zigbee Metering Plug

Drzwi Biuro

Drzwi Giętarka

Drzwi Hala

Drzwi Social

Hub

Kompresor

Motion Biuro

Multisensor Ogród

Temp Biuro

Tuya Zigbee Metering Plug

Włącznik Laser

dev:552023-05-13 07:48:00.058traceKompresor Malarnia sendZigbeeCommands : [he raw 0x40A5 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200]

dev:552023-05-13 07:48:00.028debugKompresor Malarnia polling all 0x0B04 attributes

dev:552023-05-13 07:48:00.026debugKompresor Malarnia polling.. refreshAll is false

dev:552023-05-13 07:48:00.022debugKompresor Malarnia autoPoll()

dev:552023-05-13 07:47:33.472traceKompresor Malarnia sendZigbeeCommands : [he raw 0x40A5 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200, he raw 0x40A5 1 0x01 0x0702 {10 00 00 00 00}, delay 200, he rattr 0x40A5 0x01 6 0 {}, delay 2000]

dev:552023-05-13 07:47:33.442debugKompresor Malarnia polling all 0x0B04 attributes

dev:552023-05-13 07:47:33.440debugKompresor Malarnia polling.. refreshAll is true

dev:552023-05-13 07:47:33.438infoKompresor Malarnia refresh()...

dev:552023-05-13 07:47:00.055traceKompresor Malarnia sendZigbeeCommands : [he raw 0x40A5 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200]

dev:552023-05-13 07:47:00.027debugKompresor Malarnia polling all 0x0B04 attributes

dev:552023-05-13 07:47:00.026debugKompresor Malarnia polling.. refreshAll is false

dev:552023-05-13 07:47:00.022debugKompresor Malarnia autoPoll()

dev:552023-05-13 07:46:00.062traceKompresor Malarnia sendZigbeeCommands : [he raw 0x40A5 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200]

dev:552023-05-13 07:46:00.032debugKompresor Malarnia polling all 0x0B04 attributes

dev:552023-05-13 07:46:00.031debugKompresor Malarnia polling.. refreshAll is false

dev:552023-05-13 07:46:00.027debugKompresor Malarnia autoPoll()

dev:552023-05-13 07:45:00.100traceKompresor Malarnia sendZigbeeCommands : [he raw 0x40A5 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200]

Yep. the device is offline at the moment.. :frowning:

Did you pair it again to HE ?
You can also switch off the 'Automatic Polling' option, this device should report the parameters automatically.

Yes i paired it and it was found. so its in range.
Switch back to old driver ad change to new one?
Worked before:)

Try pairing it again, currently, nothing is received from the device...
Do you have a C-8 or a C-7 hub?

If paired successfully (and if the device stays connected), you should see debug log messages coming automatically from this device, even when using the HE inbuilt 'Device' driver.

C8
Maybe there is need to reset the device itself. There is a switch pairing/work on it.
I deleted the device and switched to pairing and it was found now it cant connect to hub.

Yeah Ill re pair it but later on another tasks at hand.

1 Like

Do you have a second device using this driver? I see another “Tuya Zigbee Metering Plug” in your previous post…

Maybe you are looking at wrong device / wrong logs?

Ok, just update the driver again when you start making new tests later today.

1 Like

Yes its updated

device successfully reconected and online:) manual on off is shown in the driver...

logs i believe that the power metering is not working correct the compressor turn on but no consumption was indicated

logs after on
Logs

  • 1

  • Live

dev:562023-05-13 10:47:15.911infoKompresor malarnia breaker id = 1650812160

dev:562023-05-13 10:47:15.906debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 018C13030010455455312D494F542D5A696762656500, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[01, 8C, 13, 03, 00, 10, 45, 54, 55, 31, 2D, 49, 4F, 54, 2D, 5A, 69, 67, 62, 65, 65, 00]]

dev:562023-05-13 10:47:15.899debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 018C13030010455455312D494F542D5A696762656500

dev:562023-05-13 10:47:15.866infoKompresor malarnia (18) AlarmSet2 : 67174575

dev:562023-05-13 10:47:15.862debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 018B1200000C0101006403010113040100AF, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[01, 8B, 12, 00, 00, 0C, 01, 01, 00, 64, 03, 01, 01, 13, 04, 01, 00, AF]]

dev:562023-05-13 10:47:15.852debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 018B1200000C0101006403010113040100AF

dev:562023-05-13 10:47:15.815infoKompresor malarnia RTX (06) Phase A : [01, 8A, 06, 00, 00, 08, 09, 2E, 00, 00, 00, 00, 00, 00] value=2057

dev:562023-05-13 10:47:15.810debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 018A06000008092E000000000000, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[01, 8A, 06, 00, 00, 08, 09, 2E, 00, 00, 00, 00, 00, 00]]

1 Like

Successfully pairing the device again is a piece of very good news! A simple ZIgbee pairing became a problem lately ... : (

I see the voltage reading ( 235.0 V), but to get more from this device I will need more logs...
Does it have a load? Is the load only on Phase A or on the 3 phases ? What is the approximately load value in Watts ( V/A ) ?

1 Like

The decoding of the voltage, current and power is now available in the Tuya Zigbee Metering Plug (w/ healthStatus) ver. 1.7.6 2023-05-13

Your device is sending the voltage readings only, the current and the power are zeroes, don't know why... Let me know if you see any power readings later.

1 Like

Thanks I'll check it today

Yeah, it's not sending any wats or amps...Updated driver... Its 8 Kw compressor it turns on in a cycle, but no readings received while active.

Logs
dev:562023-05-15 12:50:28.826traceKompresor malarnia sendZigbeeCommands : [he raw 0xDDC4 1 0x01 0x0B04 {10 00 00 0B 05 05 05 08 05}, delay 200, he raw 0xDDC4 1 0x01 0x0702 {10 00 00 00 00}, delay 200, he rattr 0xDDC4 0x01 6 0 {}, delay 2000]

dev:562023-05-15 12:50:28.771debugKompresor malarnia polling all 0x0B04 attributes

dev:562023-05-15 12:50:28.770debugKompresor malarnia polling.. refreshAll is true

dev:562023-05-15 12:50:28.767infoKompresor malarnia refresh()...

dev:562023-05-15 12:50:28.633infoKompresor malarnia RTX(19) breaker id = ETU1-IOT-Zigbee)

dev:562023-05-15 12:50:28.624debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB213030010455455312D494F542D5A696762656500, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, B2, 13, 03, 00, 10, 45, 54, 55, 31, 2D, 49, 4F, 54, 2D, 5A, 69, 67, 62, 65, 65, 00]]

dev:562023-05-15 12:50:28.619debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB213030010455455312D494F542D5A696762656500

dev:562023-05-15 12:50:28.606infoKompresor malarnia Under Voltage Threshold is 175 enabled:ON

dev:562023-05-15 12:50:28.603infoKompresor malarnia Over Voltage Threshold is 275 enabled:ON

dev:562023-05-15 12:50:28.601infoKompresor malarnia Over Current Threshold is 100 enabled:ON

dev:562023-05-15 12:50:28.599debugKompresor malarnia RTX(18) AlarmSet2 : [EA, B1, 12, 00, 00, 0C, 01, 01, 00, 64, 03, 01, 01, 13, 04, 01, 00, AF]

dev:562023-05-15 12:50:28.596debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB11200000C0101006403010113040100AF, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, B1, 12, 00, 00, 0C, 01, 01, 00, 64, 03, 01, 01, 13, 04, 01, 00, AF]]

dev:562023-05-15 12:50:28.592debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB11200000C0101006403010113040100AF

dev:562023-05-15 12:50:28.573debugKompresor malarnia ignored power 0 W (change from 0.0 is less than 1 W)

dev:562023-05-15 12:50:28.571infoKompresor malarnia DinRail(06) Active. Power : 0 W (raw 0)

dev:562023-05-15 12:50:28.569debugKompresor malarnia ignored amperage 0 A (change from 0.0 is less than 25 mA)

dev:562023-05-15 12:50:28.567infoKompresor malarnia RTX (06) Phase A Current : 0 V (raw 0)

dev:562023-05-15 12:50:28.505infoKompresor malarnia voltage is 227 V

dev:562023-05-15 12:50:28.503infoKompresor malarnia RTX (06) Phase A Voltage : 227 V (raw 2270)

dev:562023-05-15 12:50:28.501debugKompresor malarnia RTX (06) Phase A combined reporting data: [EA, B0, 06, 00, 00, 08, 08, DE, 00, 00, 00, 00, 00, 00]

dev:562023-05-15 12:50:28.498debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB00600000808DE000000000000, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, B0, 06, 00, 00, 08, 08, DE, 00, 00, 00, 00, 00, 00]]

dev:562023-05-15 12:50:28.494debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAB00600000808DE000000000000

dev:562023-05-15 12:50:28.447infoKompresor malarnia RTX(09) Fault : 0

dev:562023-05-15 12:50:28.443debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAF0905000100, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, AF, 09, 05, 00, 01, 00]]

dev:562023-05-15 12:50:28.438debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAF0905000100

dev:562023-05-15 12:50:28.396debugKompresor malarnia Kompresor malarnia energy is 0.0 kWh (no change)

dev:562023-05-15 12:50:28.394debugKompresor malarnia energy_total=0.08, state.lastResetEnergy=0.08

dev:562023-05-15 12:50:28.392infoKompresor malarnia (01) Forward/Real Energy : 8 raw

dev:562023-05-15 12:50:28.388debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAE0102000400000008, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, AE, 01, 02, 00, 04, 00, 00, 00, 08]]

dev:562023-05-15 12:50:28.383debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAE0102000400000008

dev:562023-05-15 12:50:28.340debugKompresor malarnia (16) switch : 1

dev:562023-05-15 12:50:28.336debugKompresor malarnia parse: Desc Map: [raw:catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAD1001000101, profileId:0104, clusterId:EF00, clusterInt:61184, sourceEndpoint:01, destinationEndpoint:01, options:0040, messageType:00, dni:DDC4, isClusterSpecific:true, isManufacturerSpecific:false, manufacturerId:0000, command:02, direction:01, data:[EA, AD, 10, 01, 00, 01, 01]]

dev:562023-05-15 12:50:28.331debugKompresor malarnia parse: description is catchall: 0104 EF00 01 01 0040 00 DDC4 01 00 0000 02 01 EAAD1001000101

1 Like