Thermostat Scheduler sending unrequested Temps when changing Fan mode only

Thermostat Scheduler sending unrequested Temps when changing Fan mode only
10/12/22
Platform Version: 2.3.3.130
Hardware Version: Rev C-7

My goal with the HE Thermostat Scheduler is to have it switch the fan to circulate overnight and return to auto in the morning since temps are already scheduled for 74 Night and 76 Day in the thermostat but cannot schedule the Fan mode there.

The problem is Thermostat Scheduler is sending the “manual” temp along with the Fan mode change when it's working.

Logs:
app:6752022-10-12 07:30:00.290 AMinfoThermostat Fan Mode auto from Time Schedule
app:6752022-10-12 07:30:00.229 AMinfoCooling Setpoint 75.0 from Time Schedule
app:6752022-10-11 09:30:00.274 PMinfoCooling Setpoint 75.0 from Time Schedule

app:6752022-10-11 07:30:00.325 AMinfoThermostat Fan Mode auto from Time Schedule
app:6752022-10-11 07:30:00.243 AMinfoCooling Setpoint 75.0 from Time Schedule
Thermostat Scheduler missed Sending the 9:30 PM 2022-10-11 circulate command

app:6752022-10-10 07:30:00.317 AMinfoThermostat Fan Mode auto from Time Schedule
app:6752022-10-10 07:30:00.242 AMinfoCooling Setpoint 75.0 from Time Schedule
app:6752022-10-09 09:30:00.331 PMinfoThermostat Fan Mode circulate from Time Schedule

Driver:
Using Generic z-wave thermostat driver on a Honeywell thermostat
Current States
• coolingSetpoint : 75
• heatingSetpoint : 64
• supportedThermostatFanModes : ["auto","on","circulate"]
• supportedThermostatModes : ["heat","cool","off"]
• temperature : 75
• thermostatFanMode : auto
• thermostatMode : cool
• thermostatOperatingState : idle
• thermostatSetpoint : 75

Settings:

Thanks for any feedback.

I see Platform Version 2.3.3.132 has released and has some Therm Schedular changes so loaded it and will monitor further.

Did you at one time have a Cooling Setpoint in the table of 75° ? That might explain it, although I would agree that it should not be sending one. I will look into this further.

Hi and thanks for the quick reply.
No I never entered anything in except Fan modes and times in the "Select Period Settings" table.

Also version 2.3.3.132 has not changed anything for my situation.
Logs:
2022-10-13 07:30:00.420 AMinfoThermostat Fan Mode auto from Time Schedule
2022-10-13 07:30:00.296 AMinfoCooling Setpoint 75.0 from Time Schedule
2022-10-12 09:30:00.727 PMinfoThermostat Fan Mode circulate from Time Schedule
2022-10-12 09:30:00.467 PMinfoCooling Setpoint 75.0 from Time Schedule

Thanks for your help.

Check out latest release, just out. Should fix this.

I just saw that and am taking the update now.

Thanks, I'll let you know

Thank you for the fix it works as expected.

2022-10-14 07:30:00.400 AMinfoThermostat Fan Mode auto from Time Schedule
2022-10-13 09:30:00.594 PMinfoThermostat Fan Mode circulate from Time Schedule