I have a community app and driver for my Honeywell EvoHome heating system that is not maintained. This is the EU/UK version of Total Connect Comfort. Someone ported them over from SmartThings and it works great/has never thrown an error. My issue is the logging for both the app and the driver. There is no way in the preferences to disable it and so I get two lines in the logs every minute for the app and two lines every minute for the driver (per heating zone). I have 8 zones so my logs are spammed with 18 lines per minute. Everything runs well but it means when I have an issue with another app I don't get much history as this app and driver are filling it.
I'm wondering if whether anyone can advise by perusing the output I get and the code, if there's something I can leave there but comment out in some way to stop the logs (if I had an issue I could just restore the code to diagnose)
This is the output I get from the driver once a minute for every zone that uses it:
and this is the driver code:
Summary
* Copyright 2016 David Lomas (codersaur)
* Name: Evohome Heating Zone
* Author: David Lomas (codersaur)
* Date: 2016-04-08
* Version: 0.09
* Description:
* - This device handler is a child device for the Evohome (Connect) SmartApp.
* - For latest documentation see: https://github.com/codersaur/SmartThings
* Version History:
* 2016-04-08: v0.09
* - calculateOptimisations(): Fixed comparison of temperature values.
* 2016-04-05: v0.08
* - New 'Update Refresh Time' setting from parent to control polling after making an update.
* - setThermostatMode(): Forces poll for all zones to ensure new thermostatMode is updated.
* 2016-04-04: v0.07
* - generateEvent(): hides events if name or value are null.
* - generateEvent(): log.info message for new values.
* 2016-04-03: v0.06
* - Initial Beta Release
* To Do:
* - Clean up device settings (preferences). Hide/Show prefSetpointDuration input dynamically depending on prefSetpointMode. - If supported for devices???
* - When thermostat mode is away or off, heatingSetpoint overrides should not allowed (although setting while away actually works). Should warn at least.
* License:
* Licensed under the Apache License, Version 2.0 (the "License"); you may not use this file except
* in compliance with the License. You may obtain a copy of the License at:
* http://www.apache.org/licenses/LICENSE-2.0
* Unless required by applicable law or agreed to in writing, software distributed under the License is distributed
* on an "AS IS" BASIS, WITHOUT WARRANTIES OR CONDITIONS OF ANY KIND, either express or implied. See the License
* for the specific language governing permissions and limitations under the License.
metadata {
definition (name: "Evohome Heating Zone", namespace: "codersaur", author: "David Lomas") {
capability "Actuator"
capability "Sensor"
capability "Refresh"
capability "Temperature Measurement"
// capability "Thermostat"
capability "Thermostat Heating Setpoint"
capability "Thermostat Setpoint"
capability "Thermostat Mode"
capability "Thermostat Operating State"
//command "poll" // Polling
command "refresh" // Refresh
command "setHeatingSetpoint" // Thermostat
command "raiseSetpoint" // Custom
command "lowerSetpoint" // Custom
command "setThermostatMode" // Thermostat
command "cycleThermostatMode" // Custom
command "off" // Thermostat
command "heat" // Thermostat
command "auto" // Custom
command "away" // Custom
command "economy" // Custom
command "dayOff" // Custom
command "custom" // Custom
command "resume" // Custom
command "boost" // Custom
command "suppress" // Custom
command "generateEvent" // Custom
command "test" // Custom
attribute "temperature","number" // Temperature Measurement
attribute "heatingSetpoint","number" // Thermostat
attribute "thermostatSetpoint","number" // Thermostat
attribute "thermostatSetpointMode", "string" // Custom
attribute "thermostatSetpointUntil", "string" // Custom
attribute "thermostatSetpointStatus", "string" // Custom
attribute "thermostatMode", "string" // Thermostat
attribute "thermostatOperatingState", "string" // Thermostat
attribute "thermostatStatus", "string" // Custom
attribute "scheduledSetpoint", "number" // Custom
attribute "nextScheduledSetpoint", "number" // Custom
attribute "nextScheduledTime", "string" // Custom
attribute "optimisation", "string" // Custom
attribute "windowFunction", "string" // Custom
tiles(scale: 2) {
// Main multi
multiAttributeTile(name:"multi", type:"thermostat", width:6, height:4) {
tileAttribute("device.temperature", key: "PRIMARY_CONTROL") {
attributeState("default", label:'${currentValue}°', unit:"C")
// Up and Down buttons:
//tileAttribute("device.temperature", key: "VALUE_CONTROL") {
// attributeState("VALUE_UP", action: "raiseSetpoint")
// attributeState("VALUE_DOWN", action: "lowerSetpoint")
// Operating State - used to get background colour when type is 'thermostat'.
tileAttribute("device.thermostatStatus", key: "OPERATING_STATE") {
attributeState("Heating", backgroundColor:"#ffa81e", defaultState: true)
attributeState("Idle (Auto)", backgroundColor:"#44b621")
attributeState("Idle (Custom)", backgroundColor:"#44b621")
attributeState("Idle (Day Off)", backgroundColor:"#44b621")
attributeState("Idle (Economy)", backgroundColor:"#44b621")
attributeState("Idle (Away)", backgroundColor:"#44b621")
attributeState("Off", backgroundColor:"#269bd2")
//tileAttribute("device.thermostatMode", key: "THERMOSTAT_MODE") {
// attributeState("off", label:'${name}')
// attributeState("away", label:'${name}')
// attributeState("auto", label:'${name}')
// attributeState("economy", label:'${name}')
// attributeState("dayOff", label:'${name}')
// attributeState("custom", label:'${name}')
//tileAttribute("device.heatingSetpoint", key: "HEATING_SETPOINT") {
// attributeState("default", label:'${currentValue}', unit:"C")
//tileAttribute("device.coolingSetpoint", key: "COOLING_SETPOINT") {
// temperature tile:
valueTile("temperature", "device.temperature", width: 2, height: 2, canChangeIcon: true) {
state("temperature", label:'${currentValue}°', unit:"C", icon:"st.Weather.weather2",
backgroundColors:[
// Celsius
[value: 0, color: "#153591"],
[value: 7, color: "#1e9cbb"],
[value: 15, color: "#90d2a7"],
[value: 23, color: "#44b621"],
[value: 28, color: "#f1d801"],
[value: 35, color: "#d04e00"],
[value: 37, color: "#bc2323"]
// thermostatSetpoint tiles:
valueTile("thermostatSetpoint", "device.thermostatSetpoint", width: 3, height: 1) {
state "thermostatSetpoint", label:'Setpoint: ${currentValue}°', unit:"C"
valueTile("thermostatSetpointStatus", "device.thermostatSetpointStatus", width: 3, height: 1, decoration: "flat") {
state "thermostatSetpointStatus", label:'${currentValue}', backgroundColor:"#ffffff"
standardTile("raiseSetpoint", "device.thermostatSetpoint", width: 1, height: 1, decoration: "flat") {
state "setpoint", action:"raiseSetpoint", icon:"st.thermostat.thermostat-up"
standardTile("lowerSetpoint", "device.thermostatSetpoint", width: 1, height: 1, decoration: "flat") {
state "setpoint", action:"lowerSetpoint", icon:"st.thermostat.thermostat-down"
standardTile("resume", "device.resume", width: 1, height: 1, decoration: "flat") {
state "default", action:"resume", label:'Resume', icon:"st.samsung.da.oven_ic_send"
standardTile("boost", "device.boost", inactiveLabel: false, decoration: "flat", width: 1, height: 1) {
state "default", action:"boost", label:'Boost' // icon TBC
standardTile("suppress", "device.suppress", inactiveLabel: false, decoration: "flat", width: 1, height: 1) {
state "default", action:"suppress", label:'Suppress' // icon TBC
// thermostatMode/Status Tiles:
// thermostatStatus (also incorporated into the multi tile).
valueTile("thermostatStatus", "device.thermostatStatus", height: 1, width: 6, decoration: "flat") {
state "thermostatStatus", label:'${currentValue}', backgroundColor:"#ffffff"
// Single thermostatMode tile that cycles between all modes (too slow).
// To Do: Update with Evohome-specific modes:
standardTile("thermostatMode", "device.thermostatMode", inactiveLabel: false, decoration: "flat") {
state "off", action:"cycleMode", nextState: "updating", icon: "st.thermostat.heating-cooling-off"
state "heat", action:"cycleMode", nextState: "updating", icon: "st.thermostat.heat"
state "cool", action:"cycleMode", nextState: "updating", icon: "st.thermostat.cool"
state "auto", action:"cycleMode", nextState: "updating", icon: "st.thermostat.auto"
state "auxHeatOnly", action:"cycleMode", icon: "st.thermostat.emergency-heat"
state "updating", label:"Working", icon: "st.secondary.secondary"
// Individual Mode tiles:
standardTile("auto", "device.auto", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"auto", icon: "st.thermostat.auto"
standardTile("away", "device.away", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"away", label:'Away' // icon TBC
standardTile("custom", "device.custom", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"custom", label:'Custom' // icon TBC
standardTile("dayOff", "device.dayOff", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"dayOff", label:'Day Off' // icon TBC
standardTile("economy", "device.economy", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"economy", label:'Economy' // icon TBC
standardTile("off", "device.off", inactiveLabel: false, decoration: "flat", width: 2, height: 2) {
state "default", action:"off", icon:"st.thermostat.heating-cooling-off"
// Other tiles:
standardTile("refresh", "device.thermostatMode", inactiveLabel: false, decoration: "flat") {
state "default", action:"refresh.refresh", icon:"st.secondary.refresh"
standardTile("test", "device.test", width: 1, height: 1, decoration: "flat") {
state "default", label:'Test', action:"test"
main "temperature"
details(
"multi",
"thermostatSetpoint","raiseSetpoint","boost","resume",
"thermostatSetpointStatus","lowerSetpoint","suppress","refresh",
"auto","away","custom","dayOff","economy","off"
preferences {
section { // Setpoint Adjustments:
input title: "Setpoint Duration", description: "Configure how long setpoint adjustments are applied for.", displayDuringSetup: true, type: "paragraph", element: "paragraph"
input 'prefSetpointMode', 'enum', title: 'Until', description: '', options: ["Next Switchpoint", "Midday", "Midnight", "Duration", "Permanent"], defaultValue: "Next Switchpoint", required: true, displayDuringSetup: true
input 'prefSetpointDuration', 'number', title: 'Duration (minutes)', description: 'Apply setpoint for this many minutes', range: "1..1440", defaultValue: 60, required: true, displayDuringSetup: true
//input 'prefSetpointTime', 'time', title: 'Time', description: 'Apply setpoint until this time', required: true, displayDuringSetup: true
input title: "Setpoint Temperatures", description: "Configure preset temperatures for the 'Boost' and 'Suppress' buttons.", displayDuringSetup: true, type: "paragraph", element: "paragraph"
input "prefBoostTemperature", "string", title: "'Boost' Temperature", defaultValue: "21.5", required: true, displayDuringSetup: true // use of 'decimal' input type in devices is currently broken.
input "prefSuppressTemperature", "string", title: "'Suppress' Temperature", defaultValue: "15.0", required: true, displayDuringSetup: true // use of 'decimal' input type in devices is currently broken.
* Test Commands:
* test()
* Test method, called from test tile.
def test() {
//log.debug "$device.displayName: test(): Properties: ${properties}"
//log.debug "$device.displayName: test(): Settings: ${settings}"
//log.debug "$device.displayName: test(): State: ${state}"
* Setup and Configuration Commands:
* installed()
* Runs when the app is first installed.
* When a device is created by a SmartApp, settings are not populated
* with the defaultValues configured for each input. Therefore, we
* populate the corresponding state.* variables with the input defaultValues.
def installed() {
log.debug "${app.label}: Installed with settings: ${settings}"
state.installedAt = now()
// These default values will be overwritten by the Evohome SmartApp almost immediately:
state.debug = false
state.updateRefreshTime = 5 // Wait this many seconds after an update before polling.
state.zoneType = 'RadiatorZone'
state.minHeatingSetpoint = formatTemperature(5.0)
state.maxHeatingSetpoint = formatTemperature(35.0)
state.temperatureResolution = formatTemperature(0.5)
state.windowFunctionTemperature = formatTemperature(5.0)
state.targetSetpoint = state.minHeatingSetpoint
// Populate state.* with default values for each preference/input:
state.setpointMode = getInputDefaultValue('prefSetpointMode')
state.setpointDuration = getInputDefaultValue('prefSetpointDuration')
state.boostTemperature = getInputDefaultValue('prefBoostTemperature')
state.suppressTemperature = getInputDefaultValue('prefSuppressTemperature')
* updated()
* Runs when device settings are changed.
def updated() {
if (state.debug) log.debug "${device.label}: Updating with settings: ${settings}"
// Copy input values to state:
state.setpointMode = settings.prefSetpointMode
state.setpointDuration = settings.prefSetpointDuration
state.boostTemperature = formatTemperature(settings.prefBoostTemperature)
state.suppressTemperature = formatTemperature(settings.prefSuppressTemperature)
* SmartApp-Child Interface Commands:
* generateEvent(values)
* Called by parent to update the state of this child device.
void generateEvent(values) {
log.info "${device.label}: generateEvent(): New values: ${values}"
if(values) {
values.each { name, value ->
if ( name == 'minHeatingSetpoint'
|| name == 'maxHeatingSetpoint'
|| name == 'temperatureResolution'
|| name == 'windowFunctionTemperature'
|| name == 'zoneType'
|| name == 'locationId'
|| name == 'gatewayId'
|| name == 'systemId'
|| name == 'zoneId'
|| name == 'schedule'
|| name == 'debug'
|| name == 'updateRefreshTime'
// Internal state only.
state."${name}" = value
else { // Attribute value, so generate an event:
if (name != null && value != null) {
sendEvent(name: name, value: value, displayed: true)
else { // If name or value is null, set displayed to false,
// otherwise the 'Recently' view on smartphone app clogs
// up with empty events.
sendEvent(name: name, value: value, displayed: false)
// Reset targetSetpoint (used by raiseSetpoint/lowerSetpoint) if heatingSetpoint has changed:
if (name == 'heatingSetpoint') {
state.targetSetpoint = value
// Calculate derived attributes (order is important here):
calculateThermostatOperatingState()
calculateThermostatStatus()
calculateThermostatSetpointStatus()
* Capability-related Commands:
* poll()
* Polls the device. Required for the "Polling" capability
void poll() {
if (state.debug) log.debug "${device.label}: poll()"
parent.poll(state.zoneId)
* refresh()
* Refreshes values from the device. Required for the "Refresh" capability.
void refresh() {
if (state.debug) log.debug "${device.label}: refresh()"
sendEvent(name: 'thermostatSetpointStatus', value: 'Updating', displayed: false)
* setThermostatMode(mode, until=-1)
* Set thermostat mode until specified time.
* mode: Possible values: 'auto','off','away','dayOff','custom', or 'economy'.
* until: (Optional) Time to apply mode until, can be either:
* - Date: Date object representing when override should end.
* - ISO-8601 date string, in format "yyyy-MM-dd'T'HH:mm:ssXX", e.g.: "2016-04-01T00:00:00Z".
* - String: 'permanent'.
* - Number: Duration in hours if mode is 'economy', or days if mode is 'away'/'dayOff'/'custom'.
* Duration will be rounded down to align with Midnight i nthe local timezone
* (e.g. a duration of 1 day will end at midnight tonight). If 0, mode is permanent.
* If duration is not specified, a default value is used from the Evohome SmartApp settings.
* Notes: 'Auto' and 'Off' modes are always permanent.
* Thermostat mode is a property of the temperatureControlSystem (i.e. Evohome controller).
* Therefore changing the thermostatMode will affect all zones associated with the same controller.
* Example usage:
* setThermostatMode('off', 0) // Set off mode permanently.
* setThermostatMode('away', 1) // Set away mode for one day (i.e. until midnight tonight).
* setThermostatMode('dayOff', 2) // Set dayOff mode for two days (ends tomorrow night).
* setThermostatMode('economy', 2) // Set economy mode for two hours.
def setThermostatMode(String mode, until=-1) {
log.info "${device.label}: setThermostatMode(Mode: ${mode}, Until: ${until})"
// Send update via parent:
if (!parent.setThermostatMode(state.systemId, mode, until)) {
// Wait a few seconds as it takes a while for Evohome to update setpoints in response to a mode change.
pseudoSleep(state.updateRefreshTime * 1000)
parent.poll(0) // Force poll for all zones as thermostatMode is a property of the temperatureControlSystem.
return null
else {
log.error "${device.label}: setThermostatMode(): Error: Unable to set thermostat mode."
return 'error'
* setHeatingSetpoint(setpoint, until=-1)
* Set heatingSetpoint until specified time.
* setpoint: Setpoint temperature, e.g.: "21.5". Can be a number or string.
* If setpoint is outside allowed range (i.e. minHeatingSetpoint to
* maxHeatingSetpoint) it will be re-written to the appropriate limit.
* until: (Optional) Time to apply setpoint until, can be either:
* - Date: date object representing when override should end.
* - String: 'nextSwitchpoint', 'midnight', 'midday', or 'permanent'.
* - Number: duration in minutes (from now). 0 = permanent.
* If not specified, setpoint duration will default to the
* behaviour defined in the device settings.
* Example usage:
* setHeatingSetpoint(21.0) // Set until <device default>.
* setHeatingSetpoint(21.0, 'nextSwitchpoint') // Set until next scheduled switchpoint.
* setHeatingSetpoint(21.0, 'midnight') // Set until midnight.
* setHeatingSetpoint(21.0, 'permanent') // Set permanently.
* setHeatingSetpoint(21.0, 0) // Set permanently.
* setHeatingSetpoint(21.0, 6) // Set for 6 hours.
* setHeatingSetpoint(21.0, '2016-04-01T00:00:00Z') // Set until specific time.
def setHeatingSetpoint(setpoint, until=-1) {
if (state.debug) log.debug "${device.label}: setHeatingSetpoint(Setpoint: ${setpoint}, Until: ${until})"
// Clean setpoint:
setpoint = formatTemperature(setpoint)
if (Float.parseFloat(setpoint) < Float.parseFloat(state.minHeatingSetpoint)) {
log.warn "${device.label}: setHeatingSetpoint(): Specified setpoint (${setpoint}) is less than zone's minimum setpoint (${state.minHeatingSetpoint})."
setpoint = state.minHeatingSetpoint
else if (Float.parseFloat(setpoint) > Float.parseFloat(state.maxHeatingSetpoint)) {
log.warn "${device.label}: setHeatingSetpoint(): Specified setpoint (${setpoint}) is greater than zone's maximum setpoint (${state.maxHeatingSetpoint})."
setpoint = state.maxHeatingSetpoint
// Clean and parse until value:
def untilRes
Calendar c = new GregorianCalendar()
def tzOffset = location.timeZone.getOffset(new Date().getTime()) // Timezone offset to UTC in milliseconds.
// If until has not been specified, determine behaviour from device state.setpointMode:
if (-1 == until) {
switch (state.setpointMode) {
case 'Next Switchpoint':
until = 'nextSwitchpoint'
break
case 'Midday':
until = 'midday'
break
case 'Midnight':
until = 'midnight'
break
case 'Duration':
until = state.setpointDuration ?: 0
break
case 'Time':
// TO DO : construct time, like we do for midnight.
// settings.prefSetpointTime appears to return an ISO dateformat string.
// However using an input of type "time" causes HTTP 500 errors in the IDE, so disabled for now.
// If time has passed, then need to make it the next day.
if (state.debug) log.debug "${device.label}: setHeatingSetpoint(): Time: ${state.SetpointTime}"
break
case 'Permanent':
until = 'permanent'
break
default:
break
if ('permanent' == until || 0 == until) {
untilRes = 0
else if (until instanceof Date) {
untilRes = until
else if ('nextSwitchpoint' == until) {
untilRes = new Date().parse("yyyy-MM-dd'T'HH:mm:ssXX", device.currentValue('nextScheduledTime'))
else if ('midday' == until) {
untilRes = new Date().parse("yyyy-MM-dd'T'HH:mm:ssXX", new Date().format("yyyy-MM-dd'T'12:00:00XX", location.timeZone))
else if ('midnight' == until) {
c.add(Calendar.DATE, 1 ) // Add one day to calendar and use to get midnight in local time:
untilRes = new Date().parse("yyyy-MM-dd'T'HH:mm:ssXX", c.getTime().format("yyyy-MM-dd'T'00:00:00XX", location.timeZone))
else if (until ==~ /\d+.*T.*/) { // until is a ISO-8601 date string, so parse:
untilRes = new Date().parse("yyyy-MM-dd'T'HH:mm:ssXX", until)
else if (until.isNumber()) { // until is a duration in minutes, so construct date from now():
// Evohome supposedly only accepts setpoints for up to 24 hours, so we should limit minutes to 1440.
// For now, just pass any duration and see if Evohome accepts it...
untilRes = new Date( now() + (Math.round(until) * 60000) )
else {
log.warn "${device.label}: setHeatingSetpoint(): until value could not be parsed. Setpoint will be applied permanently."
untilRes = 0
log.info "${device.label}: setHeatingSetpoint(): Setting setpoint to: ${setpoint} until: ${untilRes}"
if (!parent.setHeatingSetpoint(state.zoneId, setpoint, untilRes)) {
// Command was successful, but it takes a few seconds for the Evohome cloud service to update with new values.
// Meanwhile, we know the new setpoint and thermostatSetpointMode anyway:
sendEvent(name: 'heatingSetpoint', value: setpoint)
sendEvent(name: 'thermostatSetpoint', value: setpoint)
sendEvent(name: 'thermostatSetpointMode', value: (0 == untilRes) ? 'permanentOverride' : 'temporaryOverride' )
sendEvent(name: 'thermostatSetpointUntil', value: (0 == untilRes) ? null : untilRes.format("yyyy-MM-dd'T'HH:mm:00XX", TimeZone.getTimeZone('UTC')))
return null
else {
log.error "${device.label}: setHeatingSetpoint(): Error: Unable to set heating setpoint."
return 'error'
* clearHeatingSetpoint()
* Clear the heatingSetpoint. Will return heatingSetpoint to scheduled value.
* thermostatSetpointMode should return to "followSchedule".
def clearHeatingSetpoint() {
log.info "${device.label}: clearHeatingSetpoint()"
if (!parent.clearHeatingSetpoint(state.zoneId)) {
// to update the zone status with the new heatingSetpoint.
// Meanwhile, we know the new thermostatSetpointMode is "followSchedule".
sendEvent(name: 'thermostatSetpointMode', value: 'followSchedule')
// sleep command is not allowed in SmartThings, so we use psuedoSleep().
return null
else {
log.error "${device.label}: clearHeatingSetpoint(): Error: Unable to clear heating setpoint."
return 'error'
* raiseSetpoint()
* Raise heatingSetpoint and thermostatSetpoint.
* Increments by state.temperatureResolution (usually 0.5).
* Called by raiseSetpoint tile.
void raiseSetpoint() {
if (state.debug) log.debug "${device.label}: raiseSetpoint()"
def mode = device.currentValue("thermostatMode")
def targetSp = new BigDecimal(state.targetSetpoint)
def tempRes = new BigDecimal(state.temperatureResolution) // (normally 0.5)
def maxSp = new BigDecimal(state.maxHeatingSetpoint)
if ('off' == mode || 'away' == mode) {
log.warn "${device.label}: raiseSetpoint(): thermostat mode (${mode}) does not allow altering the temperature setpoint."
else {
targetSp += tempRes
if (targetSp > maxSp) {
targetSp = maxSp
state.targetSetpoint = targetSp
log.info "${device.label}: raiseSetpoint(): Target setpoint raised to: ${targetSp}"
runIn(3, "alterSetpoint", [overwrite: true]) // Wait three seconds in case targetSetpoint is changed again.
* lowerSetpoint()
* Lower heatingSetpoint and thermostatSetpoint.
* Called by lowerSetpoint tile.
void lowerSetpoint() {
if (state.debug) log.debug "${device.label}: lowerSetpoint()"
def minSp = new BigDecimal(state.minHeatingSetpoint)
log.warn "${device.label}: lowerSetpoint(): thermostat mode (${mode}) does not allow altering the temperature setpoint."
else {
targetSp -= tempRes
if (targetSp < minSp) {
targetSp = minSp
log.info "${device.label}: lowerSetpoint(): Target setpoint lowered to: ${targetSp}"
* alterSetpoint()
* Proxy command called by raiseSetpoint and lowerSetpoint, as runIn
* cannot pass targetSetpoint diretly to setHeatingSetpoint.
private alterSetpoint() {
if (state.debug) log.debug "${device.label}: alterSetpoint()"
setHeatingSetpoint(state.targetSetpoint)
* Convenience Commands:
* These commands alias other commands with preset parameters.
void resume() {
if (state.debug) log.debug "${device.label}: resume()"
void auto() {
if (state.debug) log.debug "${device.label}: auto()"
setThermostatMode('auto')
void heat() {
if (state.debug) log.debug "${device.label}: heat()"
void off() {
if (state.debug) log.debug "${device.label}: off()"
setThermostatMode('off')
void away(until=-1) {
if (state.debug) log.debug "${device.label}: away()"
setThermostatMode('away', until)
void custom(until=-1) {
if (state.debug) log.debug "${device.label}: custom()"
setThermostatMode('custom', until)
void dayOff(until=-1) {
if (state.debug) log.debug "${device.label}: dayOff()"
setThermostatMode('dayOff', until)
void economy(until=-1) {
if (state.debug) log.debug "${device.label}: economy()"
setThermostatMode('economy', until)
void boost() {
if (state.debug) log.debug "${device.label}: boost()"
setHeatingSetpoint(state.boostTemperature)
void suppress() {
if (state.debug) log.debug "${device.label}: suppress()"
setHeatingSetpoint(state.suppressTemperature)
* Helper Commands:
* pseudoSleep(ms)
* Substitute for sleep() command.
private pseudoSleep(ms) {
def start = now()
while (now() < start + ms) {
// Do nothing, just wait.
* getInputDefaultValue(inputName)
* Get the default value for the specified input.
private getInputDefaultValue(inputName) {
if (state.debug) log.debug "${device.label}: getInputDefaultValue()"
def returnValue
properties.preferences?.sections.each { section ->
section.input.each { input ->
if (input.name == inputName) {
returnValue = input.defaultValue
return returnValue
* formatTemperature(t)
* Format temperature value to one decimal place.
* t: can be string, float, bigdecimal...
* Returns as string.
private formatTemperature(t) {
//return Float.parseFloat("${t}").round(1)
//return String.format("%.1f", Float.parseFloat("${t}").round(1))
return Float.parseFloat("${t}").round(1).toString()
* formatThermostatModeForDisp(mode)
* Translate SmartThings values to display values.
private formatThermostatModeForDisp(mode) {
if (state.debug) log.debug "${device.label}: formatThermostatModeForDisp()"
switch (mode) {
case 'auto':
mode = 'Auto'
break
case 'economy':
mode = 'Economy'
break
case 'away':
mode = 'Away'
break
case 'custom':
mode = 'Custom'
break
case 'dayOff':
mode = 'Day Off'
break
case 'off':
mode = 'Off'
break
default:
mode = 'Unknown'
break
return mode
* calculateThermostatOperatingState()
* Calculates thermostatOperatingState and generates event accordingly.
private calculateThermostatOperatingState() {
if (state.debug) log.debug "${device.label}: calculateThermostatOperatingState()"
def tOS
if ('off' == device.currentValue('thermostatMode')) {
tOS = 'off'
else if (device.currentValue("temperature") < device.currentValue("thermostatSetpoint")) {
tOS = 'heating'
else {
tOS = 'idle'
sendEvent(name: 'thermostatOperatingState', value: tOS)
* calculateOptimisations()
* Calculates if optimisation and windowFunction are active
* and generates events accordingly.
* This isn't going to be 100% perfect, but is reasonably accurate.
private calculateOptimisations() {
if (state.debug) log.debug "${device.label}: calculateOptimisations()"
def newOptValue = 'inactive'
def newWdfValue = 'inactive'
// Convert temp values to BigDecimals for comparison:
def heatingSp = new BigDecimal(device.currentValue('heatingSetpoint'))
def scheduledSp = new BigDecimal(device.currentValue('scheduledSetpoint'))
def nextScheduledSp = new BigDecimal(device.currentValue('nextScheduledSetpoint'))
// def windowTemp = new BigDecimal(state.windowFunctionTemperature)
def windowTemp = new BigDecimal(state.windowFunctionTemperature ?: formatTemperature(5.0))
if ('auto' != device.currentValue('thermostatMode')) {
// Optimisations cannot be active if thermostatMode is not 'auto'.
else if ('followSchedule' != device.currentValue('thermostatSetpointMode')) {
// Optimisations cannot be active if thermostatSetpointMode is not 'followSchedule'.
// There must be a manual override.
else if (heatingSp == scheduledSp) {
// heatingSetpoint is what it should be, so no reason to suspect that optimisations are active.
else if (heatingSp == nextScheduledSp) {
// heatingSetpoint is the nextScheduledSetpoint, so optimisation is likely active:
newOptValue = 'active'
else if (heatingSp == windowTemp) {
// heatingSetpoint is the windowFunctionTemp, so windowFunction is likely active:
newWdfValue = 'active'
sendEvent(name: 'optimisation', value: newOptValue)
sendEvent(name: 'windowFunction', value: newWdfValue)
* calculateThermostatStatus()
* Calculates thermostatStatus and generates event accordingly.
* thermostatStatus is a text summary of thermostatMode and thermostatOperatingState.
private calculateThermostatStatus() {
if (state.debug) log.debug "${device.label}: calculateThermostatStatus()"
def newThermostatStatus = ''
def thermostatModeDisp = formatThermostatModeForDisp(device.currentValue('thermostatMode'))
def setpoint = device.currentValue('thermostatSetpoint')
if ('Off' == thermostatModeDisp) {
newThermostatStatus = 'Off'
else if('heating' == device.currentValue('thermostatOperatingState')) {
newThermostatStatus = "Heating to ${setpoint}° (${thermostatModeDisp})"
else {
newThermostatStatus = "Idle (${thermostatModeDisp})"
sendEvent(name: 'thermostatStatus', value: newThermostatStatus)
* calculateThermostatSetpointStatus()
* Calculates thermostatSetpointStatus and generates event accordingly.
* thermostatSetpointStatus is a text summary of thermostatSetpointMode and thermostatSetpointUntil.
* It also indicates if 'optimisation' or 'windowFunction' is active.
private calculateThermostatSetpointStatus() {
if (state.debug) log.debug "${device.label}: calculateThermostatSetpointStatus()"
def newThermostatSetpointStatus = ''
def setpointMode = device.currentValue('thermostatSetpointMode')
newThermostatSetpointStatus = 'Off'
else if ('away' == device.currentValue('thermostatMode')) {
newThermostatSetpointStatus = 'Away'
else if ('active' == device.currentValue('optimisation')) {
newThermostatSetpointStatus = 'Optimisation Active'
else if ('active' == device.currentValue('windowFunction')) {
newThermostatSetpointStatus = 'Window Function Active'
else if ('followSchedule' == setpointMode) {
newThermostatSetpointStatus = 'Following Schedule'
else if ('permanentOverride' == setpointMode) {
newThermostatSetpointStatus = 'Permanent'
else {
def untilStr = device.currentValue('thermostatSetpointUntil')
if (untilStr) {
//def nowDate = new Date()
// thermostatSetpointUntil is an ISO-8601 date format in UTC, and parse() seems to assume date is in UTC.
def untilDate = new Date().parse("yyyy-MM-dd'T'HH:mm:ssXX", untilStr)
def untilDisp = ''
if (untilDate.format("u") == new Date().format("u")) { // Compare day of week to current day of week (today).
untilDisp = untilDate.format("HH:mm", location.timeZone) // Same day, so just show time.
else {
untilDisp = untilDate.format("HH:mm 'on' EEEE", location.timeZone) // Different day, so include name of day.
newThermostatSetpointStatus = "Temporary Until ${untilDisp}"
else {
newThermostatSetpointStatus = "Temporary"
sendEvent(name: 'thermostatSetpointStatus', value: newThermostatSetpointStatus)
Around line 353 I tried changing 'Displayed: true' to 'Displayed: false' but it made no difference. I'm not sure whether that should have worked. Maybe I'd need to delete the heating zones and re run from scratch to get the change to occur. Any ideas appreciated - I'm clueless with code.