Hi again, I have an air compressor in my shop with plumbing throughout my yard.

It uses a switch like this one...

https://www.amazon.com/LF10-4H-Pressure-Compressor-Replacement-Control/dp/B07RGZ44ZN?crid=YER85XLHNI7T&dib=eyJ2IjoiMSJ9.A2OzGy5h4YAPVtn7ZRZi29PHbB0M9i4MhllHA2GMy7ODkC7qEX7rA7_n6zJVtoV8HTBRSsNIKmDrQMm2IqgGWIHoNC3yNwA8jL0Q1BNJNOD33tFsvukSubADSy7vrv_wzSAdOGDZvHYbh1cb7x6zAgzakekrwgKAjLYTK6BeQaM0bu5LtW_byfdjocqDPqVriiE76pcpixJU-Cnx2HZBi72kyZerMZx0E7qLDnIZsDJl3NVNe2Yn6jGxZevsjEDh2wHPJmhQop9n85fIAmR8CgpQcSgh-Hqce2HolFwmHto.5X-sFCRoPGSByKfw0fANs8xyGl7KC0L58CSNLtD8PGM&dib_tag=se&keywords=electric%2Bair%2Bcompressor%2Bswitch&qid=1789772683&sprefix=electric%2Bair%2Bcompressor%2Bswitch%2Caps%2C189&sr=8-6&th=1

When you activate the lever to turn it off (or the pressure exceeds the set pressure), it opens a valve to bleed air between the compressor and the tank check valve so the next time it wants to start the pump, the pump doesn't have to work so hard to start up.

Does anyone know of a way this can be automated? I like not to re-invent the wheel if something already exists out there.

One approach is to use a couple of solenoids to pull the lever on and off, then use 2 inching relays to activate the solenoid.

Another way would be to make a servo motor (or something similar) to drive the lever on and off.

The lever looks to travel about an inch, so that is a long way for a solenoid.

If anyone has any ideas I'd like to hear them.

Thanks, Mark.

Not a "bolt on" solution, but the Aqara T1 Valve Controller will translate a ZigBee signal to a mechanical movement that may work for you. :thinking:

Why are you trying to control this vs just switching power on and off via a smart plug or a contactor?

This as you note is a safety device for the compressor, and I would hesitate to bypass this or trust a smart device in all situations. Simply cutting line power via a smart plug would seem to be simpler and safer.

How large is the compressor? 240v or 120v?

The compressor motor label reads 230V 15A, 5HP single phase.

I have been noodling using a Zigbee 30A Smart Relay (wired in line to a dumb outlet).

I wasn't comfortable turning off the power and leaving the pressure relief thingy unchanged, but I can't think of why.

If the pressure is high the regulator will work as normal so OK, if the pressure is low, I think the check valve will prevent pressure building up on the compressor, again, OK.

Maybe that is the way to go.

Thanks, Mark.