There have been a couple of old threads about HVAC filter monitoring --
Those threads are long closed.
I will give the topic another shot. I see manometers with a 0-10V output on AliExpress which seem like they could be ZWave connected. -1 to 1 Kpa with 0 - 10V output. $50. I wondered if anybody had done anything with differential pressure monitoring for their AC filter beyond the old threads that I found. There is even an RS485 option -- https://www.aliexpress.us/item/3256810349767821.html
The 0-10V route should work if you pair it with a Z-Wave module that has analog inputs. The Fibaro Smart Implant has 0-10V inputs, so it's worth checking for a current Hubitat driver before you order.
One thing to watch: the pressure drop changes a lot with fan speed. Only log readings when the blower is on the same stage, or the trend gets noisy.
I just use a google calendar event right now for reminder. I replace the 4 inch MERV 11 filter every 4 months. I would like to know what the pressure differential is. A new MERV 11 should have an initial pressure drop of 0.10 - 0.15 inches water. Replacement should be 0.40 - 0.50 inches. I guess next step is to get the $50 manual gauge and see if those estimates are anywhere close to my system.
Most industrial maintenance setups use the differential as an indicator that they need to change the filters before the reglularly scheduled interval. They do it on a timed basis or earlier if the pressure drop grows too much.
In my field we do that, or sometimes make a dynamic performance curve graph that plots current performance vs the no restrictions/base curves. It is handy for variable speed units, or multistage systems. Need continuous dP and blower data typically. Sometimes need static pressure too, depending on the system.
That is a bit of overkill for residential though. In that space I would want blower speed/stages and dP only (and zones in operation if it is a zoned system, as that changes dP significantly in most cases). Personally, I just do it based on time and move on with my life. Optimizing that $50 in filters a year isn't important to me.
NOTE: If you have a variable speed air handler, and your manufacturer is nice and exposes the RPMs as something you can monitor, you can sometimes do a very good filter monitoring estimation without adding any dP instruments at all. Depends if the handler is constant flow or RPM (there are both kinds out there on variable speed air handlers). Same form monitoring pool filters with variable speed pool pumps, just as a side note.
Kind of like the picture below (this isn't a real one, as I can't post company stuff publicly).
Then you would calculate where on the pressure vs flow you are, and plot that point on the graph too. If significantly to the left of the orange curve, performance is lacking and it is filter change time. Can often put the stall/min flow or max pressure on the graph too.
Anyway. I wouldn't do this in residential (and don't on mine), as you almost never have actual flow rate (which is needed to do that calc right). But if you are bored and want a project, and have the instrumentation/readings to do the calc in the 1st place, there ya go.
I have Hubitat control possible with my furnace. I would probably toggle the fan to manual on. That should be a consistent speed between runs. Then measure the pressure. Then turn the fan back to auto.